Discuss Tripping issue with Split load Wylex DB in the UK Electrical Forum area at ElectriciansForums.net

considering the op cant work it out poor person I love a tryer. plus a council tent .:D
buzz, you can be so cruel at times.

upload_2018-10-3_20-1-12.png
 
The OP has 2391 so should be able to do an installation resistance test if he can at least narrow the faulty circuit down and disconnect even if he feels he shouldn't be investigating further.
 
In the morning.


Switch off Main Switch and remove cover. Switch all MCB's to off. Remove the RCD load neutral cables from the neutral bars but leave all the final circuits in.
Don't worry about unplugging stuff. Set IR tester to 250v and then do global IR's N-E, removing individual neutrals if a low reading obtained to pin point. If IR satisfactory, then test between the neutral bars to check separation of circuits over the two RCD's.
 

Reply to Tripping issue with Split load Wylex DB in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock