Have it to hand when a spark is investigating - changes in IR readings may be very eye opening..........
BUT have you unplugged everything ? Washing machines? Dish washers? Ovens ?
The cooker was totally disconnected, washing machine dishwasher and tumble drier are on the kitchen circuit on the RCD that's not tripping. Just confused why after 2 years it's going ---- up
is it still ?
is it still ?
Yes, I am giving up for tonight and will take the day off tomorrow to try and sort it
Mice? water leak? trapped cable? DIY infliction?
Do you have any proper test kit?
Council property and all we got was your cooker is causing the issue. The cooker has been completely disconnected from the outlet and still it trips
That doesn't rule out the cooker circuit, isolator or outlet plate
considering the op cant work it out poor person I love a tryer. plus a council tent .:D
buzz, you can be so cruel at times.
The OP has 2391 so should be able to do an installation resistance test if he can at least narrow the faulty circuit down and disconnect even if he feels he shouldn't be investigating further.
In the morning.
Switch off Main Switch and remove cover. Switch all MCB's to off. Remove the RCD load neutral cables from the neutral bars but leave all the final circuits in.
Don't worry about unplugging stuff. Set IR tester to 250v and then do global IR's N-E, removing individual neutrals if a low reading obtained to pin point. If IR satisfactory, then test between the neutral bars to check separation of circuits over the two RCD's.