Got an issue at home, today I got home and found one of the RCD's had tripped on my split load Wylex DB.
I tried to reset but it wasn't having it. Switched all MCB's off on the RCD (Call it number 1) that had tripped then reset. All was ok, switched each MCB on and stayed in.
Put the kettle on (which is on the other RCD (call it number 2) and on the kitchen circuit) and it tripped RCD number 1, kettle carried on boiling without an issue to the RCD 2 or the MCB it is on.

House was rewired in 2016 and the new board installed then

HELP, I am at my wits end which is a very short journey

Any ideas will be greatly received. Give me 3 phase any day of the week
Wylex DB.jpg
 
Best you find a local spark with an MFT, an earth leakage clamp meter and time on his hands

Have you unplugged all items on these circuits?
All items on the circuits on the RCD have been unplugged. But still it trips when anything on the kitchen circuit is switched on. We just tried each appliance in turn and each one tripped the RCD out. Weird the mcb and RCD that protects the kitchen circuits never tripped
 
Have it to hand when a spark is investigating - changes in IR readings may be very eye opening..........

BUT have you unplugged everything ? Washing machines? Dish washers? Ovens ?
The cooker was totally disconnected, washing machine dishwasher and tumble drier are on the kitchen circuit on the RCD that's not tripping. Just confused why after 2 years it's going ---- up
 
Have it to hand when a spark is investigating - changes in IR readings may be very eye opening..........

BUT have you unplugged everything ? Washing machines? Dish washers? Ovens ?
The cooker was totally disconnected, washing machine dishwasher and tumble drier are on the kitchen circuit on the RCD that's not tripping. Just confused why after 2 years it's going ---- up
is it still ?
is it still ?
Yes, I am giving up for tonight and will take the day off tomorrow to try and sort it
 
The cooker was totally disconnected, washing machine dishwasher and tumble drier are on the kitchen circuit on the RCD that's not tripping. Just confused why after 2 years it's going ---- up


Yes, I am giving up for tonight and will take the day off tomorrow to try and sort it

Mice? water leak? trapped cable? DIY infliction?

Do you have any proper test kit?
 
The OP has 2391 so should be able to do an installation resistance test if he can at least narrow the faulty circuit down and disconnect even if he feels he shouldn't be investigating further.
 
In the morning.


Switch off Main Switch and remove cover. Switch all MCB's to off. Remove the RCD load neutral cables from the neutral bars but leave all the final circuits in.
Don't worry about unplugging stuff. Set IR tester to 250v and then do global IR's N-E, removing individual neutrals if a low reading obtained to pin point. If IR satisfactory, then test between the neutral bars to check separation of circuits over the two RCD's.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Newmarket, Suffolk

Thread Information

Title
Tripping issue with Split load Wylex DB
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34
Unsolved
--

Advert

Thread statistics

Created
ipd1961,
Last reply from
telectrix,
Replies
34
Views
4,322

Advert

Back
Top