G
Gary latto
Hi r2 end to end is 0.84
you are excused due to the fact that you are in Devon. too much time smuggling booze and hanging pirates.Ignore me, listen to Tel, I mis read your line and neutral end to end readings. The r1 seems to be right, as Tel said it's the rN that needs investigating, again a loose connection could quite easily be the cause.
The 1.66 (or 1.67 if you want to round up the recurring figure) comes from the difference in the cross sectional area of the live conductors and cpc. 2.5 (mm2) / 1.5 (mm2) = 1.666666666 (recurring).
So r2 should be 1.66 x greater than r1 (and rN).
Hope that makes sense.
smuggling booze
I always preferred vulgar fractions 2.5/1.5===5/3yeah, it's that tricky maths again. 1.6666666666 rounded up to 1 67. was much easier when we had roman numerals. XVIIIIIIIIIIIIIVIII.
WonderfulI always preferred vulgar fractions 2.5/1.5===5/3
(then reminding your common sense 0.99999999 .. =1)
so a third is 0.333333333 ..