• If you have electrical work available, then you are in the correct forum.

    Post details of the position you have on offer in this forum. Domestic / homeowners are also welcome to post electrical work they have available on their property. Or you're welcome to seach for a Local Electrician in our directory.

Discuss The old one still learning in the Electricians Jobs area at ElectriciansForums.net

This electrician job is going for grabs, please don't post contact details in this area of the forum. Use the forum messaging system instead.
Hi telectrix I understand the cpc would be 1.67x greater due to only 1.5 , so yes like you say 0.5 x1.67 =0.83 .
But totally confused with regards the 1.66 calculation
So like you say the phase and cpc seem fine so neutral problem am I still looking at a bad connection do you think ?
 
Ignore me, listen to Tel, I mis read your line and neutral end to end readings. The r1 seems to be right, as Tel said it's the rN that needs investigating, again a loose connection could quite easily be the cause.

The 1.66 (or 1.67 if you want to round up the recurring figure) comes from the difference in the cross sectional area of the live conductors and cpc. 2.5 (mm2) / 1.5 (mm2) = 1.666666666 (recurring).

So r2 should be 1.66 x greater than r1 (and rN).

Hope that makes sense.
 
yep.might just be a terminal screw a bit loose in a socket. any why the confusion with 1.66? it's the ratio of 1.5/2.5.
 
Ignore me, listen to Tel, I mis read your line and neutral end to end readings. The r1 seems to be right, as Tel said it's the rN that needs investigating, again a loose connection could quite easily be the cause.

The 1.66 (or 1.67 if you want to round up the recurring figure) comes from the difference in the cross sectional area of the live conductors and cpc. 2.5 (mm2) / 1.5 (mm2) = 1.666666666 (recurring).

So r2 should be 1.66 x greater than r1 (and rN).

Hope that makes sense.
you are excused due to the fact that you are in Devon. too much time smuggling booze and hanging pirates.
 
my favorite tipple at my old local was Addlestones cloudy cider on draft. 7%. only 2 of us drank it, but we got through 2 x 10 gallons a week between us. sadly my mate has moved to a better world, having been crushed between a 50ft. canal barge and a lock when pi$$ed.
 
yeah, it's that tricky maths again. 1.6666666666 rounded up to 1 67. was much easier when we had roman numerals. XVIIIIIIIIIIIIIVIII.
 
I always preferred vulgar fractions 2.5/1.5===5/3

(then reminding your common sense 0.99999999 .. =1)
so a third is 0.333333333 ..
Spock strikes with logic yet again. but McCoy would argue that 0.3333333 is not a turd. it's life Jim, but not as we know it. (enter the Borg).
 
think this thread has fractionally run it's course.
 
how is 1/6 related to 20%?
If you know the gross figure (net+vat) divide it by 6 and times 1 to give you the VAT... Not so relevant now as 20% is easy to work with, but when it was 17.5%, you'd divide by 47 and times by 7 for the VAT element. Or times by 40 instead to give you the Net element.

Far easier than multiplying the gross by 0.148936 to give you the VAT.

Fractions are very useful things... as are feet and inches but that's a different topic...
 

Reply to The old one still learning in the Electricians Jobs area at ElectriciansForums.net

Similar Threads

M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Replies
1
Views
296
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
737
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock