I have just had a rental property tested. The electrician says my consumer unit needs replacing as it is not split load.i am only using 5ways of the current consumer unit and all cct,s are rcd protected. Is this correct?
Are you the landlord or the tenant?
 
I am the landlord. I have an electrical background but not domestic so am unsure of the current regs. The installation is as Anthonybragg describes. All other parts of the installation have passed other than the split load issue. Seems a little over the top for five cct terraced house!
 
In fairness there is no requirement to record the Regulation numbers against the observations in the Report.

I did not say there was a requirement :(

If he has a schedule of inspections he should be able to note the number of the particular regulation where a non conformity occured against the coding given for any problems
It would indicate why the inspector feels it does not comply
 
Can the main RCD be changed back to a main switch and then the 5 circuit breakers changed for RCBO's?
As the other's have said,it's more of a convenience issue rather than a safety issue.It's the OP's call.
 
I am the landlord. I have an electrical background but not domestic so am unsure of the current regs. The installation is as Anthonybragg describes. All other parts of the installation have passed other than the split load issue. Seems a little over the top for five cct terraced house!
What code is placed against this issue ? As said above, any competent inspector would have noted this as a C3 at most.
 
The term split load is also incorrect.

I beg to differ.How is it incorrect?
Screwfix sell MK SPLIT LOAD boards here?
 
Split load generally referred to part non rcd and part rcd. Your pic is generally referred to as dual rcd. The OPs board has five circuits so I suspect his terminology is at odds with what he means.
 
No cert has been issued yet. Just told over the phone. Was going to do the work myself then he’d retest and issue the cert. wanted to make sure the work was necessary because of time and cost
 
Split load refers to having two separately controlled supplies(either rcd or non rcd protected) fed via one main switch.If the OP had a split load board fitted then 2 circuits would be on one rcd and 3 circuits on the other.(Quite often i find that when separating the circuits in a 5 way board that there is usually a extra circuit that has been popped into say a 32 amp breaker with the ring.When fitting the new board,this extra circuit can go on its own 16 amp breaker and you'll end up with 3 circuits on one side and 3 on the other)
 
One question that has come into my head is that has it got an RCD as the main switch because it is a TT supply?
 
The chances are,if a new consumer unit be fitted it will likely be a metal clad number with two Rcds to split the circuits

In my own opinion the system you have currently is safer than whats presently permitted for TT systems
That is because the casing has the potential to become live with no protection by disconnection required
By that I mean no protection other than what they seem to term "enhanced protection" a sort of clamping or support to the tails to prevent the possible nasty fault occurring where a live exposed tails can touch the metal,perhaps just relying on only the supply fuse to hopefully pop

There again you could fit a Rcd before the tails to better protect,but don't you already have that?:)
 