Hi all changed over some old 2D emergencies 11 in total for LED. They are controlled from some time lag switches on a communal staircase. But as soon as I powered up the lights all flash randomly. Had it before when one has flashed and just changed when to an incandescent but never had them all flashing any ideas anyone. Cant leave them with a disco for long
 
If the time lag switches are pneumatic replace with standard switches and see if that resolves it. I assume the charge indication remains on.
 
Yes the charge light stays on. The time lag switches are touch not pneumatic. It's got me really baffled

Do they have a neutral at the switches?

If they don't then they probably take power from L and S/L by passing a small current through the load to neutral. Far too small a current to cause a normal load to react, but plenty enough to charge capacitors in the LED driver circuits.
Obviously when the capacitors have charged they will then discharge via the LED causing it to flash.
 
Not checked the switches yet tbh so not sure. If that's the case will I get away with changing one fitting back to 2D to stop it

If your contract is to replace them with LED units then no you can't just fit a 2D fitting,plus then you'd have one odd fitting out which doesn't match any of the others creating a maintainence headache.

If the switches are the source of the problem you could replace them for switches which don't cause this, or fit a small resistive load device such as the Danlers 'resloade' or 'resload' for the unenclosed version.
 
If your contract is to replace them with LED units then no you can't just fit a 2D fitting,plus then you'd have one odd fitting out which doesn't match any of the others creating a maintainence headache.

If the switches are the source of the problem you could replace them for switches which don't cause this, or fit a small resistive load device such as the Danlers 'resloade' or 'resload' for the unenclosed version.
Cheers davesparks ordered a load today sure they can live with a couple of flashing lights for a few days.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cheshire
Business Name
Stay Switched On

Thread Information

Title
Flashing LED emergencies
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
Daveh36,
Last reply from
littlespark,
Replies
11
Views
1,213

Advert

Back
Top