Guest viewing limit reached
I have 3 circuits (microwave, disposal, and dishwasher) entering a metal box where the THHN wire will be spliced to Romex.
I spent half an hour reading 2020 NEC Article 250 but didn't see multiple circuits specifically addressed.
To ground the box do I just need to pigtail off of one circuit's ground wire and attach to the box, or do I pigtail all 3 circuits' ground wires together?
In case you're wondering, the conduit is metal, which I believe is sufficient for grounding, but I don't trust all of the mechanical joints nor the fittings' set screws.
Noah pig tail all the grounds to the box and you will be good
Cool, thanks.
Another question that I realize I need an answer to - should I pigtail all of the neutrals together?
I have a feeling NEC says no, but on the plus side, the extra copper would reduce voltage drop when less than full load capacity is being utilized, and it would be a wash if all circuits were fully utilized.
Cool, thanks.
No, never join neutrals from different circuits together, this creates a very dangerous hazard for anyone working on the circuit in the future.
Cool, thanks.
Yes you need to pig tail all the whites together also
They are from different circuits!!
If the THHN is the feed for the 3 appliances you would probably have 1 hot 1 neutral and one ground coming from the panel you would have to tie all the neutrals together. If 3 separate feeds that would be different. It sounds to me like all 3 appliances are on the same circuit. Noah how many THHN wires are do you have besides the 3 cables. I’m not saying it’s the proper installation, I’m saying it sounds like there all on the same circuit
I see your point OP needs to clarify.
I hope they are not all on the same circuit- that would overload a single circuit.
The OP could have two circuits sharing one neutral (MWBC) and in such a case yes all the neutrals would be tied together in the J-box. Make sure the breaker is a double pole, or both single pole breakers have their handles tied together.
If the OP has two or more circuits each with its own neutral coming from the breaker box then yes each neutral needs to be separate in the J-box.
I guess that is a bit ambiguous.
These are three separate circuits as required by 2020 NEC, each on it's own breaker, black/white/green THHN runs for each.
I'll keep the different circuits' neutrals isolated, and thanks westward10 and Dave for pointing out the hazard of doing otherwise.
Three separate circuits, 3 separate neutrals, we are all set! :)
After further thought, I realize I really don't see the hazard in pigtailing all of the neutrals together, since they're all connected together at the neutral bus bar in the panel.
What am I missing?
What am I missing?
Noah you are not missing nothing. The panel is the first disconnect after the meter and yes the neutrals and grounds can be terminated on the same bar. Any subfed panel after your main panel you have to separate the neutrals from the grounds
I'm not talking grounds vs. neutrals.
Two people said there was a hazard in connecting the neutrals from different circuits together.
They're already connected together at the panel neutral bar, so how is the hazard created?
If you have more than 1 circuit sharing neutrals and you turn 1 breaker off to work on it the neutral will still have voltage on it from the other circuits sharing that same neutral. That’s the danger they are talking about
If the circuits are separate then keep the neutrals separate, joining them all together can create a hazard for anyone working on the circuits if they are not all isolated.
While it is not definitive, his first line is "I have three circuits..." I would take that to mean 3 individual circuits. If not, then I would expect it to be 1 circuit.
Paul
Hmm, I didn't get a reply notification; anyway
A neutral that is supposed to be dead, would now be live to whom ever is working on it. This is not to code.
How could a neutral be anything but dead when it's grounded at the panel?
Regardless, the crux of the matter which no one has addressed, is how it can make any difference if the neutrals are tied together at a junction box when they're already tied together at the panel.
[automerge]1590038053[/automerge]
I definitized it a bit later on:
In a normal circuit if a fault develops in the neutral then the circuit will stop working,someone will notice and get it fixed.
In your proposed arrangement if a fault develops in one of the neutrals the circuit will continue to work due to the other two neutrals being linked to it, however the fault will cause those two neutrals will be overloaded, but nobody will notice due to everything working. This overload could then lead, ultimately, to a fire.
Any GFCI (RCD) installed now or in the future to protect the circuit will trip instantly due to the imbalance caused by the joining of the neutrals.
Anybody working on the installation in the future will be unaware of this arrangement being in place, expecially considering it is specifically prohibited by your electrical code.
Open a neutral under load, and it will float up to 120 volts.
Yes, normally that would happen on the load side of the break.
However the proposed situation of joining three neutrals together would prevent the voltage rise from occurring, but it would overload the other two neutrals.
Yup, that is unless someone shut down the microwave circuit un-doing the wire nuts thinking they are all dead. This is why the NEC requires any branch circuit sharing a neutral be equipped with listed handle ties or a multi pole breaker.
Mountain View, CA
United States of America
Correct grounding of metal junction box w/splices for 3 circuits
USA Electrical Forum
Noah Katz,
Cookie,
USA Electrical Advice
Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This is the main UK Electrical Forum at ElectriciansForums.net. Electrician Laws and Regulations related to Electrics and Electricals within the United Kingdom. Electrician talk, questions and answers can be found in our UK electrical forum.