T
TPES
Just thought id post a photo or 2 of an intake, I will need to do a PIR on the whold building.
Just from the photos what can you find to put a code to and why..??
One of you may spot something i have missed.. (infact im certain of it!)
Thers no isolator for the supply...
Each phase to the meter then out the henley blocks, split upto the consumer units..
Surely they should have an isolator? should i recommend there be one installed ?
isolators are not deemed necessary unless the cable is over 3m long...! normally just fitted to ease hassle in long run!
Bit of rats nest in those pictures was wondering if the tails looped into the MEM switch fuse then onto the henleys. Think I would want one personally :)
The phases are split a total of 9 times, but im not sure what phase is doing which CU's...
I've also got to work out the Max demand in KVA also, not sure where to start as many of the CU's not marked up very well and not clear whats what..
Any pointers on where to start..
I have a full list of what Fuses/breakers are in each CU
start with the pricing pad!!! and mutter the words 15k... :) :D
do one phase at a time! i find a marker pen and phase tape come in handy!
So ideally the phases will be split as evenly as possible, but it looks like theres more CU's on the yellow phase than any other..
So i really need to get a maximum demand with diversty applied for each phase.
Then with the 3 figures i end up with i can work out total KVA?
The customer and DNO are on my case as they needed to know the KVA yesterday.
Ive not had to work out the KVA on 3 phase before, so sorry if the questions are obvious to many of you