H
HossUK
Hi Guys,
I am looking for a bit of advice.
I am a landlord of a 1st floor flat in a small purpose-built block built in the mid eighties I think.
I have just had an EICR and have been cited C2s on the following :--
5.11 Provision of additional protection by 30mA RCD (See Note), c) For Cables concealed in walls / partitions at a depth of less than 50mm
Observation: No rcd present - C2
What are the likely cables are they talking about here?
7 Current-using equipment
7.2 Equipment does not constitute a fire hazard
Observation: bare connector blocks connecting the en-suite down-lights and smoke detector (which is in the hallway not in the en-suite - c2)
What sort of connectors should be used if these constitute a fire hazard?
8 Locations containing a bath or shower
8.4 Presence of supplementary bonding conductors unless not required by BS7671:2018
Observation: not present with no rcd protection - C2
Can you enlighten me on this one?
Do these items sound like Legitimate C2's ??? Or is someone trying to get some work out of me? Because they have included a quote of £718 to resolve the 'urgent issues'. There were a few C3's as will including no RCD but I was expecting that.
If these issues are just 'touting for work' should I report it? If so who do you suggest I report to?