carrying out an eicr on a building recently we found the external ze reading to be extremely low ie 0.02ohms. so by measurement and testing are fault current read 20ka. now most of the mcbs rcbos ets have an icn of 10kohms. this poses a problem as obvisoluy the mcbs etc would self destruct under fault conditions. what would you code this and more importantly how would we rectify this problem, Interested to here your thoughts.
 
2 options available,

1 extend the supply cable by running a length of swa from incomer to fuseboard, 50m would probably bring the reading down enough.

2 change the breakers to a higher rating of fault current.
 
Wilco it is pretty close to the sub station however I've always been a great believer the meter never lies even checked the meter on my cal card all readings very accurate.
 
I had a case where I was measuring about 3m away from transformer and the meter was giving readings that were far higher than I expected.
changed the values on cert. to what the transformer manufacturer stated.
 
are you suggesting I cheat and higher the ze reading. ha ha
not cheat,
figure can be found by measurement or investigation.

if the transformer manufacturer says max pfc is 20Ka and the meter reads 92Ka then the manufacturer wins on my paperwork.

all the meters suggest that they may be inaccurate when close to transformer but not 1 of them says in the instructions that below x meters away you should ignore the reading on meter!!
 
Julie were would I find the let through value and are you talking about the main incomer fuses
Yes, so if they are say bs88 industrial fuses, anything below about 125A would be less than 10kA let through for 20kA perspective.

You need the manufacturer's data, there will be a curve showing this data, select 20kA on the prospective axis and follow it until it reaches the appropriate fuse line/curve then on the other axis you can read the actual let through current
 
Here's an example if you select 20kA on the lhs and go across to the 100A fuse line, then follow it down - or up, it gives a let through of 9kAScreenshot_20201022-204047_Drive.jpg
 
ok I understand that thank you. so the breakers in the dbs that we have tested are all Schneider type, and there all 10ka breaking capacity and with a fault current of 20ka. so if I look into the let through value and that's above 10ka im happy to code 2 it. But if the client asks how we resolve it were do I go with it . thanks in advance