Most EICs for DB changes would not meet the requirements for the landlord regulations.
A rewire or new build EIC is the best of all worlds of course, since it should confirm that cables are correctly routed within zones, properly erected, supported, etc. That is almost always a limitation on a consumer unit change EIC, but also on most if not all EICRs too for practical reasons.
So there is probably an argument that a very thorough EIC which clearly states that it inspected 100% of the installation would be no less safe than an EICR and would comply with the spirit of the legislation regarding testing the installation.
However, the letting agent can't be expected to make that judgement so will fall back on the Government guidance, which states that since it hasn't been rewired or newly built, that an EICR is required.
With most certificate software, it takes minutes to convert one to the other, since the schedule of inspections is identical (at least in my software). The only difference is that the number of LIMS may well be higher on a board change compared to an EICR.
So unfortunately the simplest answer in this case is going to be to get an EICR. The electrician should understand the situation and be willing to do one, either free or for very little additional cost.
If you show him the guidance already noted above, then he may be prepared to change his mind. If not, you can ask him to produce something in writing which clarifies why he believes his certificate complies with the law - that may at least make him think about his views.
Failing that, you may be able to get one done cheaper than normal given than much of the testing and documentation work has been done, but then you are asking another inspector to rely on the word of the previous one, which can be troublesome.
A rewire or new build EIC is the best of all worlds of course, since it should confirm that cables are correctly routed within zones, properly erected, supported, etc. That is almost always a limitation on a consumer unit change EIC, but also on most if not all EICRs too for practical reasons.
So there is probably an argument that a very thorough EIC which clearly states that it inspected 100% of the installation would be no less safe than an EICR and would comply with the spirit of the legislation regarding testing the installation.
However, the letting agent can't be expected to make that judgement so will fall back on the Government guidance, which states that since it hasn't been rewired or newly built, that an EICR is required.
With most certificate software, it takes minutes to convert one to the other, since the schedule of inspections is identical (at least in my software). The only difference is that the number of LIMS may well be higher on a board change compared to an EICR.
So unfortunately the simplest answer in this case is going to be to get an EICR. The electrician should understand the situation and be willing to do one, either free or for very little additional cost.
If you show him the guidance already noted above, then he may be prepared to change his mind. If not, you can ask him to produce something in writing which clarifies why he believes his certificate complies with the law - that may at least make him think about his views.
Failing that, you may be able to get one done cheaper than normal given than much of the testing and documentation work has been done, but then you are asking another inspector to rely on the word of the previous one, which can be troublesome.