Hello all,
Just had an electrician wire in a radial circuit in my house to my loft as I use the space for my home theatre equipment & wanted a dedicated circuit for the equipment as its consists of quite a few power hungry amps & devices.
He has wired the radial in 4.0mm2 twin & earth cable connected to a 32 amp breaker, normally I gather this would not be an issue & is common place in installations.
The problem I can see is the total length of the cable from the consumer unit to the equipment in the loft is 35 meters & after doing a little research it seems that voltage drop is going to be an issue with a cable of this length.
After using a calculator online for voltage drop the conductor size required for a 6.0mm2 to be below the 5% maximum voltage drop stated in the regulations.
That calculation is for a cable that has been surface clipped which is correct for the length of the run in the loft which is 22 meters long.
The length of the run going along & up the side of the house to reach the loft is 13 meters long & is inside 25mm conduit along with a 2.5mm2 & 1.0mm2 cable for other circuits in the house.
So am I correct in saying that using a 32 amp breaker in this situation is not appropriate & a 20 amp breaker would be the correct choice?