J
jon evans
Hi Guys, Just had an EICR test and was told it will fail , but not too bad (a couple of C2s) but needs doing. Waiting for the failure cert. to show me the total work needed, and should be here tomorrow. Is there a kind soul out there who can assist me [a retired old electrician who's quite confused by all this new stuff] in fixing it ? I'm in the NW6 area in London. I can pay cash and help with stripping cables etc and supply tea or coffee and the cheese and pickle sandwiches as and when required. Please call me !
What are they providing you with, an EICR doesn't fail as such it will just be unsatisfactory. Did they hint as to what the Code 2 issues are.
When you get the report you can post it here with any personal identification blanked off (like your name, who did the EICR, etc). Maybe also a photo of any items mentioned as well if it helps understand what/why a C1/C2 has been issued.
That way you can get some feedback on what might be the best route to correcting any issues raised.
Remember, you don't need to have a replacement EICR done with a satisfactory outcome, you just need to document that the repairs have been done.
I.e. If the C1, or C2 were because of say a broken light switch or socket outlet, you could replace it yourself.
that is of course reliant on you being able to do the work correctly and if ever required to prove your competence , capable of doing so.
OK guys, many thanks for the advice and will post report when I get it. The tester did say the consumer unit
was at least 20 years old and would need updating/replacing.
The report should say what the issues are (e.g. missing RCD protection) and not how to fix it (like replace a consumer unit just because it is old). Replacing the consumer unit might be the simplest outcome, but there could be other options.
Hi
Just had a EICR fail, was told that it needs to be put on the PME system and a new CCU.
Does not specify what exactly is wrong with it. The tenant said they just spent 10 minuetes testing the sockets and left.
I am a bit suspicious.
Hi
Could you post the EICR on here for us to look at. Redact any names and addresses though.
Hi Thanks for the reply, I have attached the EICR and some photos.
  • EICR public.pdf
    EICR public.pdf
Well the supply earth is in very poor condition and definitely a C2 fault, but there is something a bit odd about it: That looks like a fairly new cutout (grey thing below your meter) but the earth connection to the supply cable does not look like something the DNO (power supply company, I'm guessing UK Power Networks for your location) would do or consider acceptable.
Unless you have electrical stuff in the bathroom and it is not properly bonded (earth wires across pipes, etc), I would dispute a C2 for no RCD protection, but for your own safety / peace of mind having RCD protection is a good thing.
Not commented on is the dangling state of the tails (black & red cables from meter to your fuse box = CU), those should be supported / clipped to the wall!
Also the test result correctly notices the hob is a C-curve 32A MCB, but the Zs limit shown is for B-curve (minor, but makes poor earth even more important to fix).
Other might notice other stuff in the EICR, but certainly you have to get the earthing sorted out ASAP.
My take on those pics: Fly-by inspection not worth the paper and whoever fitted the key meter couldn't be bothered to put the tails back behind the water pipe! Agreed the earth either needs changing to the proper clamp or more usefully moving onto PME but those are both DNO items to resolve.
If you do genuinely need (or want) RCD protection then I'd suggest one overall RCD on the incoming supply would take about 10 mins to fit and also resolve the issue of supporting the tails, although, as there's no Insulation Resistance results on the sheet then that might be a tbc.
jon evans,
ukiri,