What about the CCU, does that really need replacing?Well the supply earth is in very poor condition and definitely a C2 fault, but there is something a bit odd about it: That looks like a fairly new cutout (grey thing below your meter) but the earth connection to the supply cable does not look like something the DNO (power supply company, I'm guessing UK Power Networks for your location) would do or consider acceptable.
Unless you have electrical stuff in the bathroom and it is not properly bonded (earth wires across pipes, etc), I would dispute a C2 for no RCD protection, but for your own safety / peace of mind having RCD protection is a good thing.
Not commented on is the dangling state of the tails (black & red cables from meter to your fuse box = CU), those should be supported / clipped to the wall!
Also the test result correctly notices the hob is a C-curve 32A MCB, but the Zs limit shown is for B-curve (minor, but makes poor earth even more important to fix).
Other might notice other stuff in the EICR, but certainly you have to get the earthing sorted out ASAP.
"need" is too strong a word. To make it safe, no. But it would be advisable as the additional protection is well worth having.What about the CCU, does that really need replacing?
Thank you all for your comments they were very informative."need" is too strong a word. To make it safe, no. But it would be advisable as the additional protection is well worth having.
Had it not been for the earthing situation I would suggest many inspectors would have declared that installation to be satisfactory, assuming nothing else was missed. Not up to latest regs, but that doesn't make it unsafe.
But whatever you do with the CU, please get the earthing sorted out asap. Right now in some fault conditions there is no guarantee the supply will turn off.
I've seen a few property's in London area where the earth on the rotten old lead sheaf supply cable is failing, according to UKPN "we're not obliged to give you an earth go away" and they seem to think an underground cable with questionable earthing on the sheaf is okay. Like for example the recent notable case of sticking flamible stuff to high rise buildings It's a case of waiting for people to die then everyone who's duty it was to know and be responsible acts all surprised.I'm surprised no insulation resistance tests were carried out. The incoming water and gas pipes both appear to be metal and bonded, I would have thought the Zs readings would be much lower with these connected. The pipe clamp appears to be attached to the outer mechanical protection layers of that PILS cable rather than the lead sheath itself which might explain the high reading. There is no way the DNO would have made a connection like that.
Only option in the meantime is to TT it, so yes full RCD protected new consumer unit would be highly advisable.
They are (though not sure who would force them) - and since they have no records as to whether one was originally provided or not they could I guess claim that any TN-S clamp was not done by them. It is after all very common to see the bonding clamps used for them which is usually a DIY 'upgrade' (Though apparently they were approved for a period in the 70s)Aren't they required to maintain an earth where it has been provided?
^that, 99% of properties here have had the old sweated on wire chopped right back and a pipe clamp installed, ukpn response is "prove to us we provided an earth" which is often not possibleThey are (though not sure who would force them) - and since they have no records as to whether one was originally provided or not they could I guess claim that any TN-S clamp was not done by them. It is after all very common to see the bonding clamps used for them which is usually a DIY 'upgrade' (Though apparently they were approved for a period in the 70s)
Having said that, in the Kent/London border areas I work, they've always managed to provide PME when asked - even on overhead lines.
Had it a few times, I usually do a Ze on the cable sheath if it comes back as a viable earth then that is what I base my argument on for the DNO having provided an earth in the past or I ask them if it is normal for them to place uninsulated extraneous metalwork in a consumers premises^that, 99% of properties here have had the old sweated on wire chopped right back and a pipe clamp installed, ukpn response is "prove to us we provided an earth" which is often not possible
I guess if there is evidence of the old wire remaining that would be sufficient proof?^that, 99% of properties here have had the old sweated on wire chopped right back and a pipe clamp installed, ukpn response is "prove to us we provided an earth" which is often not possible
DNO ?I'm surprised no insulation resistance tests were carried out. The incoming water and gas pipes both appear to be metal and bonded, I would have thought the Zs readings would be much lower with these connected. The pipe clamp appears to be attached to the outer mechanical protection layers of that PILS cable rather than the lead sheath itself which might explain the high reading. There is no way the DNO would have made a connection like that.