EICR check failed

Discuss EICR check failed in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi Guys, Just had an EICR test and was told it will fail , but not too bad (a couple of C2s) but needs doing. Waiting for the failure cert. to show me the total work needed, and should be here tomorrow. Is there a kind soul out there who can assist me [a retired old electrician who's quite confused by all this new stuff] in fixing it ? I'm in the NW6 area in London. I can pay cash and help with stripping cables etc and supply tea or coffee and the cheese and pickle sandwiches as and when required. Please call me !
 
"need" is too strong a word. To make it safe, no. But it would be advisable as the additional protection is well worth having.
Had it not been for the earthing situation I would suggest many inspectors would have declared that installation to be satisfactory, assuming nothing else was missed. Not up to latest regs, but that doesn't make it unsafe.
But whatever you do with the CU, please get the earthing sorted out asap. Right now in some fault conditions there is no guarantee the supply will turn off.
Thank you all for your comments they were very informative.
 
I'm surprised no insulation resistance tests were carried out. The incoming water and gas pipes both appear to be metal and bonded, I would have thought the Zs readings would be much lower with these connected. The pipe clamp appears to be attached to the outer mechanical protection layers of that PILS cable rather than the lead sheath itself which might explain the high reading. There is no way the DNO would have made a connection like that.
I've seen a few property's in London area where the earth on the rotten old lead sheaf supply cable is failing, according to UKPN "we're not obliged to give you an earth go away" and they seem to think an underground cable with questionable earthing on the sheaf is okay. Like for example the recent notable case of sticking flamible stuff to high rise buildings It's a case of waiting for people to die then everyone who's duty it was to know and be responsible acts all surprised.

Only option in the meantime is to TT it, so yes full RCD protected new consumer unit would be highly advisable.
 
I've seen a few property's in London area where the earth on the rotten old lead sheaf supply cable is failing, according to UKPN "we're not obliged to give you an earth go away" and they seem to think an underground cable with questionable earthing on the sheaf is okay. Like for example the recent notable case of sticking flamible stuff to high rise buildings It's a case of waiting for people to die then everyone who's duty it was to know and be responsible acts all surprised.

Only option in the meantime is to TT it, so yes full RCD protected new consumer unit would be highly advisable.

Aren't they required to maintain an earth where it has been provided?
 
Aren't they required to maintain an earth where it has been provided?
They are (though not sure who would force them) - and since they have no records as to whether one was originally provided or not they could I guess claim that any TN-S clamp was not done by them. It is after all very common to see the bonding clamps used for them which is usually a DIY 'upgrade' (Though apparently they were approved for a period in the 70s)

Having said that, in the Kent/London border areas I work, they've always managed to provide PME when asked - even on overhead lines.
 
They are (though not sure who would force them) - and since they have no records as to whether one was originally provided or not they could I guess claim that any TN-S clamp was not done by them. It is after all very common to see the bonding clamps used for them which is usually a DIY 'upgrade' (Though apparently they were approved for a period in the 70s)

Having said that, in the Kent/London border areas I work, they've always managed to provide PME when asked - even on overhead lines.
^that, 99% of properties here have had the old sweated on wire chopped right back and a pipe clamp installed, ukpn response is "prove to us we provided an earth" which is often not possible
 
^that, 99% of properties here have had the old sweated on wire chopped right back and a pipe clamp installed, ukpn response is "prove to us we provided an earth" which is often not possible
Had it a few times, I usually do a Ze on the cable sheath if it comes back as a viable earth then that is what I base my argument on for the DNO having provided an earth in the past or I ask them if it is normal for them to place uninsulated extraneous metalwork in a consumers premises
 
I'm surprised no insulation resistance tests were carried out. The incoming water and gas pipes both appear to be metal and bonded, I would have thought the Zs readings would be much lower with these connected. The pipe clamp appears to be attached to the outer mechanical protection layers of that PILS cable rather than the lead sheath itself which might explain the high reading. There is no way the DNO would have made a connection like that.
DNO ?
 
I've seen a few property's in London area where the earth on the rotten old lead sheaf supply cable is failing, according to UKPN "we're not obliged to give you an earth go away" and they seem to think an underground cable with questionable earthing on the sheaf is okay. Like for example the recent notable case of sticking flamible stuff to high rise buildings It's a case of waiting for people to die then everyone who's duty it was to know and be responsible acts all surprised.

Only option in the meantime is to TT it, so yes full RCD protected new consumer unit would be highly advisable.
Could just fit an upfront rcd in a plastic enclosure
 

Reply to EICR check failed in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock