No, the live bare ends were dangling free for anyone to see or touch without removing anything.
Apologies - I was looking at the connector block photo not the loose flex, rather missing the point.
I'd like to think that I'd have spotted it in an EICR but personally I'd test as far as the FCU and anything beyond would be visual inspection unless I had reason to dig deeper. So if I saw a loose cable I'd certainly go into "I smell a rat" mode, but if it wasn't in sight I wouldn't go looking for it.
But it can't be a coincidence that the boiler failed due to that bad connection immediately after the EICR
I can see it looks suspicious but doesn't really make sense for the tester to have caused that loose connection unless they unwittingly increased tension on the cable, and it would have had to have been loose in advance.
Personally I would agree with the inspector in that any appliances are ancillary to the fixed wiring installation and that is most definitely not part of an EICR. I would like to think I would have spotted the dangly wire and maybe would have looked into that but mostly I would have been very focussed on the fixed wiring. It is a moot point I agree but given time and cost constraints especially with landlords you simply cannot cover it all. Added to that, appliances are outside the skill set of an electrician and we would generally see all boiler and controls as part of the gas safe inspection. It is not that I do not have an eye to pick up things outside of the remit it is more like my focus is not there. It is a cautionary tale though for me at least. It is very much the LL's responsibility to ensure the installation and appliances are safe. It is something you might consider taking up with your local council?
Something that may be of interest to this thread:
There is a Q and A article by ESF, on periodic inspections, that sort of suggests that EICRs should include the electrical equipment of central heating systems:
Q2.11 Are the relevant tests of regulations 643.2 to 643.11, for example continuity of protective conductors, insulation resistance and earth fault loop impedance, applicable to parts of systems such as room and cylinder thermostats, motorised valves and programmers?
Yes
Regulation number(s):
  • 411.3.1.1
  • 411.3.2
  • 643.7
https://www.-----------------------...spection-testing-certification-and-reporting/
Yes
  • 411.3.1.1
  • 411.3.2
  • 643.7
I would not feel comfortable with some of the testing recommended as above, pushing 500V through CH programmer really?, as nearly all of them are delicate electronic pieces of equipment.
I had the first EICR done on my flat last week, which failed with some C2s for having an older (2001) plastic consumer unit with no RCDs, but otherwise passed:
A couple of days later I'm called to the property due to no hot water and find the electric boiler is dead. There's a connector block in an enclosure under the boiler so I removed the faceplate to have a look and saw continuous blue sparks from a very bad connection, to say the least:
At this stage I'm already feeling aggrieved as this had worked flawlessly for 6 years and suddenly just after the EICR there's this terrible connection that can't have been sparking like that for years, and the control board in the boiler is likely blown (later confirmed).
I'm wondering why there's three neutrals jammed into the same connection and notice one is from a loose cable going down behind the hot water cylinder. Wondering where it goes I reach down to wiggle it and... BANG!
Photo isn't very clear because I've immediately switched the main switch off so it's dark. The cable had bare ends and was just dangling behind the cylinder! It had come into contact with the it as soon as I reached down and thus the bang.
The electrician who did the EICR and the agency I paid deny any responsibility for not finding any of this, saying "checking wiring centers and cables from cylinders is not part of an EICR. Inspection and testing is carried out on the fixed wiring where accessible, as far as the isolator to the heating system, which was carried out."
(The cable isn't from the cylinder and in fact has nothing to do with it.)
Is it really the case that a professional test costing hundreds of pounds isn't even expected to find a live cable with bare ends dangling in an easily-accessible location right next to the consumer unit? Just another box ticking exercise with no real assurance of the safety of the installation at all? Please forgive the rant but this could easily have electrocuted me.
I am retired now but i can assure as a QM and also did Periodic Inspection and Testing Certs myself that if i saw that i would have made quick safety mods (connectors and/or insulation tape) to ensure it was not possible to cause an electrical fire or shock risk, especially given there was no RCD protection, it is an essential need during testing to make quick safety mods to ensure risk of shock and or fire is reduced if not eliminated.
However MmMuUuuHHAHHhahAHa You must have been aware it was like this yourself ? you don't need to be qualified to know this is wrong.
No self respecting electrician would leave it like this unless he provided a quote for upgrade/repair and the works were not agreed and did not go ahead. On the up side you did request an Inspection and the company should have given you the full options of testing accompanied with costs for 20% testing of the electrical system or a FULL ON testing if it hadn't been tested since install or 5 years.
I always made it clear that 20% was the minimum and done each year so after 5 years the entire system had been checked and tested. When a car goes in for a MOT they check the whole car, not just the tires, hand brake and wipers.
i understand you are aggrieved and annoyed but most important of all you will get good advice on this forum.
Best Regards RBS Retired 17th Edition
To be fair how many people would pull a cable going down behind the tank to see it's purpose because there are several others going in the same direction, having said that it is adjacent to the consumer unit. I doubt there is one person on here who carries out EICRs on a regular basis who can claim they have never knowingly missed serious problem that includes me. I have been back to do remedials and uncovered things previously missed because I have further pulled the installation apart, something you tend not to do on an EICR.
Me neither. The current regs do allow us to reduce the test to 250V in these situations though, and would be tested combined L+N to E.
I do give the hot water and heating system a quick once-over on an EICR. It's worth it IMO as it's often not been installed by an electrician, you can often find something interesting.
I do the same nine times out of ten it is a load of unrestrained cables hanging out of a poorly connected joint box.
Any connected equipment gets to full dose of 500v and loop tests are always carried to the connected equipment.