- Dec 18, 2011
- 5,378
- 6,731
- 405,788
- United Kingdom
I have just completed an EICR.
The lighting circuit has an earth leaving the CU, then some lights have 2 core going to them (L + N) and some twin and earth, no continuity of CPC even at the ones with an earth. There are some metal light fittings that require an earth and also metal screws in the light switches. Am I right in thinking that if I change the lights to class 2 and replace screws with plastic screws then this would suffice and it would then be a C3?
Are these plastic screws readily available? They all seem to be 25mm long which would not be long enough for some of the switches.
In addition... what are peoples thoughts on imperial cable. The sockets are wired in imperial cable, therefore (thanks to @pc1966 's recent dating thread) they will be 50+ years old. IR results are 20Mohms and no green goo. I was thinking C3? I realise they pass all tests but it is very old. Perhaps you guys would not code it at all?
Cheers all.
Cheers all.