Droopy
Ok, I've got an issue I can't figure out to save my life.
Background: I'm putting in a 100a sub panel in my detached 2 car high bay garage. Other than a 50a and a 30a 240v circuit(s), everything is on 20a circuits with CAFCI/GFCI Plug on Neutral Homeline circuit breakers (https://www.homedepot.com/p/Square-...and-GFCI-Circuit-Breaker-HOM120PDFC/204844661). I've got 2 circuits going to separate single pole switches that switch several outlet in the ceiling for lights. 6 more circuits are for wall outlets (Paired outlets every 4 feet or so with power from 2 different 20a circuits.)
So, got it all done. Powered up and checked each outlet with a circuit tester. They all show hot and wired correctly. However, one of the outlet circuits (labeled "C" on the attached photo) trips when I switch on either of the switched circuits ("A" or "B"). I've swapped breakers around to make sure it's not a bad breaker. The switched circuits go up to the ceiling in EMT to a junction box where I've spliced them into Romex running to the switches and outlets. The circuit that's being tripped goes up in a completely separate EMT conduit to a separate junction box before being spliced into Romex and going to its respective outlets. The Romex for the 3 circuits is only in close proximity for about 5 total feet and I've carefully checked to make sure a staple or something hasn't damage any of the wires.
When I check the DF fault code on the breaker, it shows a ground fault. Note that it only trips when A or B is powered AND switched on.
I can't think of what else to check. Ideas?
Thanks,
John
Thanks,
JohnView attachment 90483
Since they are separate you have the two hots tied together at the light and each hot is from a different phase and that’s why it’s tripping