Ok, I've got an issue I can't figure out to save my life.

Background: I'm putting in a 100a sub panel in my detached 2 car high bay garage. Other than a 50a and a 30a 240v circuit(s), everything is on 20a circuits with CAFCI/GFCI Plug on Neutral Homeline circuit breakers (https://www.homedepot.com/p/Square-...and-GFCI-Circuit-Breaker-HOM120PDFC/204844661). I've got 2 circuits going to separate single pole switches that switch several outlet in the ceiling for lights. 6 more circuits are for wall outlets (Paired outlets every 4 feet or so with power from 2 different 20a circuits.)

So, got it all done. Powered up and checked each outlet with a circuit tester. They all show hot and wired correctly. However, one of the outlet circuits (labeled "C" on the attached photo) trips when I switch on either of the switched circuits ("A" or "B"). I've swapped breakers around to make sure it's not a bad breaker. The switched circuits go up to the ceiling in EMT to a junction box where I've spliced them into Romex running to the switches and outlets. The circuit that's being tripped goes up in a completely separate EMT conduit to a separate junction box before being spliced into Romex and going to its respective outlets. The Romex for the 3 circuits is only in close proximity for about 5 total feet and I've carefully checked to make sure a staple or something hasn't damage any of the wires.

When I check the DF fault code on the breaker, it shows a ground fault. Note that it only trips when A or B is powered AND switched on.

I can't think of what else to check. Ideas?

Thanks,

JohnProblem Breakers.jpg
 
Ok, I've got an issue I can't figure out to save my life.

Background: I'm putting in a 100a sub panel in my detached 2 car high bay garage. Other than a 50a and a 30a 240v circuit(s), everything is on 20a circuits with CAFCI/GFCI Plug on Neutral Homeline circuit breakers (https://www.homedepot.com/p/Square-...and-GFCI-Circuit-Breaker-HOM120PDFC/204844661). I've got 2 circuits going to separate single pole switches that switch several outlet in the ceiling for lights. 6 more circuits are for wall outlets (Paired outlets every 4 feet or so with power from 2 different 20a circuits.)

So, got it all done. Powered up and checked each outlet with a circuit tester. They all show hot and wired correctly. However, one of the outlet circuits (labeled "C" on the attached photo) trips when I switch on either of the switched circuits ("A" or "B"). I've swapped breakers around to make sure it's not a bad breaker. The switched circuits go up to the ceiling in EMT to a junction box where I've spliced them into Romex running to the switches and outlets. The circuit that's being tripped goes up in a completely separate EMT conduit to a separate junction box before being spliced into Romex and going to its respective outlets. The Romex for the 3 circuits is only in close proximity for about 5 total feet and I've carefully checked to make sure a staple or something hasn't damage any of the wires.

When I check the DF fault code on the breaker, it shows a ground fault. Note that it only trips when A or B is powered AND switched on.

I can't think of what else to check. Ideas?

Thanks,

JohnView attachment 90483
Since they are separate you have the two hots tied together at the light and each hot is from a different phase and that’s why it’s tripping
 

Reply to CAFCI/GFCI Gremlin on sub panel in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I had an electrician install a 100Amp subpanel which feeds a mini split. I addition I added a Homeline 50A GFCI breaker to power a shed. I...
Replies
9
Views
2K
Hello all! Newer house, original owner(Florida). no change to electrical system. Just found there was an outlet (GFCI) in the closet so I wanted...
Replies
2
Views
812
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
277
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
468

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock