Hi guys I was wondering if someone could help me, I’ve got to wire a extra switch in from a grid switch which has an emergency side and normal, I know I’ve got to take 3 browns over 2 being strippers and an earth, I was just wondering if someone could tell me the connections.

Thanks
DA34B979-0A26-47A6-8E5D-54918F08B2C5.jpeg
 
Last edited by a moderator:
The switch on the right, looking from behind, is currently a 1W light switch, and you want to make that 2W with another 2W switch added elsewhere.
Have I got that correct?
 
Does the existing grid switch have a terminal and screw in the hole next to the L1 terminal. If so, it should be labelled L2 (hidden by the wire).
 
In that case it's a one way switch, and would need replacing by the 2 way equivalent.
Once that's done, the wires that are currently in COM(mon) move to L2, and you connect your 2nd switch in parallel - COM to COM, L1 to L1, and L2 to L2.
 
That looks like singles is it tubed into that cavity box.
 
In that case it's a one way switch, and would need replacing by the 2 way equivalent.
Once that's done, the wires that are currently in COM(mon) move to L2, and you connect your 2nd switch in parallel - COM to COM, L1 to L1, and L2 to L2.
Thank you very much Brian appreciate your help
 