was asked by a freind of a friend to go look at a club he had done but not sure on the electrics so here goes;
lights keep trippinng; could have something to do with having a load of 14 amps on a 6 amp breaker even after allowing for diversity you would have to be pretty dam generous to allow for that
15 year old dimmer pack even though a new one has been paid for at the price of £15k
bar lights tripping constantly; could have something to do with the short circuit;
none of the emergency lights hold more than 20 minutes of charge;
exit stairway left with no light fitting old one taken off so it`s pitch black apart from the live cable on the wall at 6 foot that is, not terminated just dangling;
live cables from the fans hanging in disabled toilet;
socket in db room black and melted;
hole leading straight through to the alley way above the db board so rain is coming in onto the board 24" wide;
soocket fronts not been fastened up properly 20 of them that is
live cable from old sign left outside un terminated light switches have been taken off and left.
now i was thinking this looks like some sort of "sod it if they are not going to pay i am off" but it`s not i have seen the invoices for the payment of the full amount with thanks slip as well?? needless to say i have made all the bits safe when i was there but who the hell leaves a place like that knowing people are going in there?
lights keep trippinng; could have something to do with having a load of 14 amps on a 6 amp breaker even after allowing for diversity you would have to be pretty dam generous to allow for that

15 year old dimmer pack even though a new one has been paid for at the price of £15k

bar lights tripping constantly; could have something to do with the short circuit;
none of the emergency lights hold more than 20 minutes of charge;
exit stairway left with no light fitting old one taken off so it`s pitch black apart from the live cable on the wall at 6 foot that is, not terminated just dangling;
live cables from the fans hanging in disabled toilet;
socket in db room black and melted;
hole leading straight through to the alley way above the db board so rain is coming in onto the board 24" wide;
soocket fronts not been fastened up properly 20 of them that is
live cable from old sign left outside un terminated light switches have been taken off and left.
now i was thinking this looks like some sort of "sod it if they are not going to pay i am off" but it`s not i have seen the invoices for the payment of the full amount with thanks slip as well?? needless to say i have made all the bits safe when i was there but who the hell leaves a place like that knowing people are going in there?
think he had his christmas a few weeks ago looking at the bill that went in for it