Just looking to get thoughts on testing a hotel, 5 years old, 35 rooms each with sub board with 3 circuits, kitchen, boiler house, general area/office sockets. Original installation certificate is 6 pages.... and not much is marked up.
Just wanting peoples thoughts on a rough time frame for inspection and testing.
 
Just looking to get thoughts on testing a hotel, 5 years old, 35 rooms each with sub board with 3 circuits, kitchen, boiler house, general area/office sockets. Original installation certificate is 6 pages.... and not much is marked up.
Just wanting peoples thoughts on a rough time frame for inspection and testing.
So you've got 35 x 4 for rooms (inc feed), probably around another dozen in kitchen, same boiler house, same for office etc.... then you've got alarm circuits as well if included so somewhere between 175-250 circuits. A) How the heck did that lot only squeeze onto six pages originally and B) you know you've got a C3 already (labelling!). Methinks you might find some skeletons in the bodge cupboard here, so don't price too low!
 
Do you know how many circuits there are.
Rough guess, 225 circuits
40 boards

Im thinking 1-2 hour per circuit as they are not marked up. But would be way out if there is some logic behind how they have done it.
So far i know of polarity issues on es lamp holders, metallic switch faceplates not connected to CPC.
Best one so far is main switch for installation is 250 TP metal switch. No earth…
 
Rough guess, 225 circuits
40 boards

Im thinking 1-2 hour per circuit as they are not marked up. But would be way out if there is some logic behind how they have done it.
So far i know of polarity issues on es lamp holders, metallic switch faceplates not connected to CPC.
Best one so far is main switch for installation is 250 TP metal switch. No earth…
I don't think polarity on modern ES lamp holders is a concern any more?

Sounds like a bit of a lash up of an install though🫢
 
I don't think polarity on modern ES lamp holders is a concern any more?

Sounds like a bit of a lash up of an install though🫢
I don't think polarity on modern ES lamp holders is a concern any more?
Is that true, I wasn't aware of this. Would be good if true, as the idea of taking of 50-60 covers with screw heads that have been chewed up by the original installer was starting to get me down.
 
I don't think polarity on modern ES lamp holders is a concern any more?
Is that true, I wasn't aware of this. Would be good if true, as the idea of taking of 50-60 covers with screw heads that have been chewed up by the original installer was starting to get me down.
559.5.1.206 In circuits of a TN or TT system, except for E14 and E27 lampholders complying with BS EN 60238, the outer contact of every Edison screw or single centre bayonet cap type lampholder shall be connected to the neutral conductor. This regulation also applies to track mounted systems.
 
I don't think polarity on modern ES lamp holders is a concern any more?
Newer ones are OK as the shroud stops easy contact with a 'live' threaded part when changing a lamp.
Is that true, I wasn't aware of this. Would be good if true, as the idea of taking of 50-60 covers with screw heads that have been chewed up by the original installer was starting to get me down.
Is that assuming many will be wrong? The few ES holders I have dealt with had L/N identified so you hope they would be put in correct polarity automatically.

I fancied getting the Kewtech Lightmate Kit to make it easier/safer to probe bulb holders but I hardly do that work to justify it. Not sure if a non-contact voltage tester would work with one of those to confirm the centre was live and surround neutral, anyone tried it?

If they are Class I earthed holders then you can do R1+R2 to check polarity and ADS, assuming no dimmer or whatever to mess up the resistance reading.
 
. A) How the heck did that lot only squeeze onto six pages originally ce etc...and B) you know you've got a C3 already (labelling!). Methinks you might find some skeletons in the bodge cupboard here, so don't price too low!
Six page certificate is weird but, for me, the biggest factor is that the hotel is only 5 years old. For what could be a quite simple, very decent size job, a good visual before quoting should give plenty of clues to requirements.
Method of distribution to the 35 room CU's and the rest of the installation is important. Interesting to know more too, only being designed 5 years back, presumably.
But was it done by idiots?
 
Six page certificate is weird but, for me, the biggest factor is that the hotel is only 5 years old. For what could be a quite simple, very decent size job, a good visual before quoting should give plenty of clues to requirements.
Method of distribution to the 35 room CU's and the rest of the installation is important. Interesting to know more too, only being designed 5 years back, presumably.
But was it done by idiots?
Designed is maybe being generous. Not a terrible job but far from ideal.
3 Floors, each floor with own 12-18w db. (mixture of Acti9 and Eaton, which is a bit strange) each room is supplied from C32 mcb in 6mm 3 core SWA glanded at db. Each room then has a contactum main switch board with 3 type AC RCBOs, 32a for sockets, 10 for bathroom underfloor heating and 6 for lights. Unlikely for selectivity to be an issue, but I think I would have done 40a supply at mainboard or 20a radial in rooms. Also SWA at room consumer unit is not glanded. just bared back and taped up.
I would say the original contractor was maybe stretching their abilities for the job but I don't know much about the firm.
 
Looks like I was being generous. It sounds like a really poor effort.
Where are the strict standards gone which had to be met, especially for hotels.
Think I'd give it a wide birth, something isn't right.
Proper planning seems to have gone to pot.
Good luck with it.
 
Just looking to get thoughts on testing a hotel, 5 years old, 35 rooms each with sub board with 3 circuits, kitchen, boiler house, general area/office sockets. Original installation certificate is 6 pages.... and not much is marked up.
Just wanting peoples thoughts on a rough time frame for inspection and testing.
As a very rough estimate I’d be somewhere between 3500-5000 for this.

Timeframe about 2men, 4 days testing and a day for sorting paper work etc
 