HappyHippyDad
Supporter
A customer has asked me to fit an easee one EVCP. I notice that it has a type B RCD in it (I think). We are not supposed to fit a 'lower grade' RCD upstream, due to the blinding effects.
Its not possible (at least not easily) to fit a type B RCBO into the 'fusebox' branded consumer unit, so I am unsure how to proceed?
I feel I may be missing something here as there must be 1000's of easee one EVCP's fitted?
Is the RCD actually 61008 compliant?
A lot of these built in RCDs do not comply.
No it would mean the inbuilt RCD protection is not compliant with BS7671 and the CoP.
A lot of the early charger points had built in RCDs with did not satisfy EN 61008 and hence did not comply to the standards. If it does comply is RCD protection upstream necessary?
The route is through the ceiling, all the way to the outside (from consumer unit). Then in conduit to the EVCP.
It's PME, so has fault protection from ADS.
I do get a little confused about what 'doesn't' need to be RCD protected.
If you have 3 spare ways in the board, you could potentially do what I did for a heat pump circuit I worked on recently. I shortened the busbar by two modules, installed the type B RCCB in the space, and installed the circuit MCB next to it on the last 'tooth' of the busbar. The MCB fed the RCCB which then fed the circuit.
This was with fusebox gear btw.
Google AI declares the Easee RCD as being compliant with BS610081 etc, but no references.
Not being convinced, I had a further look, which revealed this... does it help?
In summary:
Crikey, so is my only option here to take up 3 ways in the consumer unit. A type B RCCB (2 ways) fed by an MCB?
I think I may try and persuade them to buy a different unit!
#7 indicates the built in RCDs satisfy the standards so an upstream RCD would not be required but I would double check your unit with the supplier.
Why do you think an upstream RCD is needed?
What type of cable and is it buried in the wall less than 50mm deep at any point?
RCD protection is not required for fault protection in this case, it's not a domestic lighting circuit and presumably the charger isn't in a bathroom so those aren't relevant.
The requirement for RCD protection of the outlet is covered by the unit itself.
In summary:
Don't forget they faced a sales ban in Sweden and their native Norway for lying about the nature of this "RCD". You definitely need to install one. It absolutely and categorically is not a BS EN 61008 or BS EN 61009 device in the EVSE.
I did wonder!
From the blurb that says it does an auto test, I assume it must be a sort of 'electronic equivalent' to mimic the characteristics of an EN61008 etc device, but not physically of traditional RCD form (and therefore not amenable to approval to that standard)
I've just had a look for the latest version of the Certificate of Conformity for the Easee One, which was issued on 21st May this year, and regarding the RCD it says this:
Residual direct current detecting device (RDC-DD) complying with IEC 62955, clause 9.9
I don't know the details of what that implies, other than the fact they can't claim compliance with the traditional RCD device standards.
I have come across this, which seems to be a description of the protection system aimed at installers
https://download.easee.com/m/31bc990e0654fd3a/original/A2g_RDC-DD Functional_Description_EN.pdf
The above does include the gem: "The charging station shall be installed with an external RCD Type A in the fixed installation."
The Easee certification claims compliance with the Electric Vehicle Charging standard, EN IEC 61851-1:2019, which embodies electrical safety, and they also claim compliance with the standard for Circuit Breakers IEC 60947-2:2016+A1:2019 (which includes those with a re-closing function),
There appears to have been type testing by TUV for this particular design of residual current circuitry, so it seems they can now legitimately CE mark the product and sell it as safe!
So following the mantra of selecting a CE approved product, and following manufacturers instructions, you could argue that despite the lack of BS EN 61008 certification for residual current circuitry, it has an alternative type approval for the bespoke device within it, so you wouldn't be doing anything wrong by installing or using it! (Except some parts of the manufacturers documentation/instructions seem to contradict each other!)
I did wonder!
Yes exactly, the RDC-DD is fine allowing use of Type A dedicated RCD interrupting all live conductors instead of Type B. It may mimic RCD functionality, but is not really an RCD - certainly not to either BS EN 61008 or BS EN 61009. It's a common problem with many EVSEs, but they shouldn't misrepresent what the internal device is.
That is what the Easee functional description of the RDC-DD says.
But it is not what the Easee charging point installation instructions say (at least the copy I read)
Part of the confusion is that Easee seem to have updated their documentation in the period Dec 24 to May25.
Including the Type A RCD in the fixed installation would surely be the way to go.
PS grumpyjohn01 was referring to installation of an ASHP where it probably required a type B device.
I would go along the lines of :
Regulation 722.531.3.101 of BS 7671:2018+A2:2022 states that unless the circuit is supplied using the protective measure of electrical separation, each charging point incorporating a socket-outlet or vehicle connector complying with the BS EN 62196 series is to be protected individually by an RCD of Type A, Type F or Type B and having a rated residual operating current not exceeding 30 mA. The RCD is also required to disconnect all live conductors.
Where have you got that from?
The OP has stated the charging point includes a B type RCD so any upstream RCD device must also be B type to function correctly and therefore comply.
Possibly my post #13 which quotes Easee's documentation on Residual Current protection, dated Dec 2024. The discussion subsequently turned to whether an RCD would be required at all at source.
If the charger already embodies an RDC-DD, why would a type B RCD also be required at the source of supply?
If the cable is buried in a wall less than 50mm deep and does not have an earthed metal protection of some sort it would be required.
Or, not applicable in the OP's case but may be for others, and RCD is required for fault protection.
Agreed - these points were made in the admittedly rather long thread above.
Having established that a (double pole) Type A RCD or RCBO seems to be needed, I just wondered why Type B was mentioned - that's all I meant!
The OP stated that the EVCP has a type B RCD in it, so we must assume that type B protection is required.
HappyHippyDad - If you haven't got fed up with this thread by now, and already turned down the job, you might be coming to the conclusion it's not perhaps as bad as you thought..
My understanding (and this might be wrong!) is that you could use a Fusebox single module width 'miniature' double pole Type A RCBO at the CU
That's assuming you are not faced with contradictory instructions accompanying the charger!
I didn't get the quote! :D
I had a sneaky feeling that they just wanted a cheap job. I very much doubt the next electrician will look into like I have in order to do a proper job. Still, you get what you pay for. it's good to lose a quote every now and then, shows your not too cheap..
Many thanks to all those who took the time to reply. You always learn something. I have learnt that I need to look into the RCD BS conformities with regards the internal RCD's of EVCP's the next time I fit one.
HappyHippyDad
Supporter
Gloucestershire
Easee one EVCP has a type B RCD fitted in it.....
HappyHippyDad,
HappyHippyDad,
