L
Lighthouse Phil
Any socket outlet, be it 2A, 5A or 13A should be protected by an RCD.
It's suppling portable appliances.
It's suppling portable appliances.
Any socket outlet, be it 2A, 5A or 13A should be protected by an RCD.
It's suppling portable appliances.
While I totally agree that any socket outlet that is being used by "ordinary persons" that do not exceed 20amps for general use, should be RCD protected, as in reg 411.3.3, this case as they are designed specifically for lights you should be able to get away without use of RCD protection. Though the RCD protection my still be needed for the cable and regulation 526.6.6.
The portable equipment again needs RCD protection if it is for use outdoors and does not exceed 32 amps, I doubt that the lamps will be used outside, but of course as the designer if you think they will be then they need to be RCD protected.
hi malc but if the cables are installed at a depth of less than 50mm and not mechanically protected for the whole of the circuit then RCD needed i think mate