Why is mains domestic power referred to as either 230v or 240v? Why not settle on just one of them? (My limited knowledge tells me that the reality is usually 243v or 237v - is that right?)

Cheers.
 
230v is to bring us in line with europe and 240 is what our power stations kick out.
 
The supply industry has actually done nothing physical to reduce the nominal supply voltage from 240V to 230V, it's still 240V open circuit at the terminals of the local supply transformer. What has changed, as part of European harmonisation (Cenelec HD472), the declared nominal voltage has changed from 240v +-6% (between 225.6 and 254.4V) to 230V +10% -6% (between 216.2 and 253V), very little change, just a slightly wider margin at the lower end. This suits the DNO's just fine as it gives them a bigger window of acceptable supply voltage in rural areas, without the associated costs rewinding transformers or tap changing.
Note:- A second round of change in the declared nominal supply voltage (Cenelec HD472-S2) 230V +-10% is pending, it was due on 1/1/2008 but has yet to be implemented in the UK.
 
Last edited by a moderator:
230v is to bring us in line with europe and 240 is what our power stations kick out.



Our power stations generally kick out 400kv. 230-240 is what you get depending on network demand and transformer tapping.
 
You can dress it up however you want to, what you have is what you have, ...and that's 415/240V
The rest is just hot air and the land of make believe!! lol!!! I guess you can call it the same as creative accounting... lol!!!:rofl:
 
ive had issues with security systems with monitored power supplies that throw a wobbly at anything over 250v and quite often see it rise to 253-255v on site in off peak times,advise customer to complain to dno and surprise theres no fault to be found but the supply voltage is a nice 235v on next visit..
 
The supply industry has actually done nothing physical to reduce the nominal supply voltage from 240V to 230V, it's still 240V open circuit at the terminals of the local supply transformer. What has changed, as part of European harmonisation (Cenelec HD472), the declared nominal voltage has changed from 240v +-6% (between 225.6 and 254.4V) to 230V +10% -6% (between 216.2 and 253V), very little change, just a slightly wider margin at the lower end. This suits the DNO's just fine as it gives them a bigger window of acceptable supply voltage in rural areas, without the associated costs rewinding transformers or tap changing.
Note:- A second round of change in the declared nominal supply voltage (Cenelec HD472-S2) 230V +-10% is pending, it was due on 1/1/2008 but has yet to be implemented in the UK.
I think you'll find that it used to be 240V + or - 10%.
The 6% only came in with the change to 230V.
If you do the calculations, you'll find both come out at 216V.
The only thing that has really changed, is that the suppliers are now not allowed to supply a voltage over 253V, whereas in the past they were allowed up to 264V.
 
I think you'll find that it used to be 240V + or - 10%.
The 6% only came in with the change to 230V.
If you do the calculations, you'll find both come out at 216V.
The only thing that has really changed, is that the suppliers are now not allowed to supply a voltage over 253V, whereas in the past they were allowed up to 264V.

The 240v +/- 6% is correct the 230v +10% was done so as not to disadvantage the uk supply industry as it lowered the allowed upper voltage marginally from 254v to 253v
 
if your filling in certs its 230v 400v as this "standard " was harmonised with the rest of europe Older sparks like myself still refer to 240 n 415 tho
 
And don't forget that 230V (400V) is the Nominal Voltage U[SUB]0[/SUB] that you use for your design calculations.
 
.....and no you can't try and cheat cable voltage drop calculations by starting off at 245V......
 