B
BillyH
What options do i have for terminating a 16mm 3 core swa into a plastic consumer unit?
In the context of mechanical or earthing ?
are you using the 3rd core as cpc? if so, then the armour only needs earthing at the supply end.
So i would'nt need to use a gland. I could just expose the conductors and connect as per mains tails
Try and fit a conduit box to the consumer unit,it can be fixed securely reducing strain on the cons unit and allow the termination of the Swa to be done
Personally i would never convert a SWA cable to T&E in an adaptable box in this circumstance. If you mount the metal adaptable box directly under the CU enclosure connected via plastic or metal coupling or other, you can then make your SWA termination off with a banjo or earthing nut to the box and take your conductors straight through to the CU, ....Sorted!!
As stated above, introducing unnecessary joints is never a good idea, especially when talking about the larger sized of domestic cables.
I've never seen street lighting with a means of earthing SWA cables without making use of a gland, and can't picture them either. you can't clamp them, without putting undue stress on the internal conductors. If anyone has a link to these accessories, i'd be interested to have a look at them.... Some of the worst corrosion i've seen on SWA cables have been at street lighting positions...
http://www.google.co.uk/url?sa=t&rc...peWdCQ&usg=AFQjCNHl3HQiAKlC_wWmKpiQT7tFuxDr6A
some of the cutouts( try the link above), come with a cone attached, and you then use a jubilee clip to terminate the armour. Ive not used them, but been on jobs where they have been used. I dont like them either, but i also hate the indoor type glands, and use CW or E1W all of the time.
billyhas, you say the SWA will be in a partition wall at first fix, will the CU be mounted surface on the board afterwards, or will it be a flush fit?
I would take it into a metal adaptable box just before the CU and then from that to the CU in T+E.
Surface mounted
Then you can't make a joint in an adaptable box that is not accessable!!!
I never intended to join the cable. I just need to terminate through the back of a plastic consumer unit
terminate into metal adaptable box, fixed flush into the stud wall with noginns top and bottom, leave the lid off and put the plasterboard on with the cables of your SWA coming through where you want, then you can surface mount the CU using the noggins top and bottom of the A/B as fixing points. simples
I apologise if there was any confusion but surely post #12 gave the info you thought was omitted until post #25.Please keep upsounds like a PLAN. funny how it's only in post #25 that we find out he wants to come into the BACK of the CU!
terminate into metal adaptable box, fixed flush into the stud wall with noginns top and bottom, leave the lid off and put the plasterboard on with the cables of your SWA coming through where you want, then you can surface mount the CU using the noggins top and bottom of the A/B as fixing points. simples