What options do i have for terminating a 16mm 3 core swa into a plastic consumer unit?
 
are you using the 3rd core as cpc? if so, then the armour only needs earthing at the supply end.
 
Hi,

You could terminate the swa into a seperate box that you would mount near the cu, then in the box, you would conect it to t&e via choc bloc, terminals etc. Then the t&e would go to the cu.

Cheers

Jay
 
just glandf the SWA into the CU, and then use a banjo, bent at 90deg to allow lug to be attched inside of the CU. This will reduce your Zs, and will take an extra few seconds. its not good practice to introduce joins in a cable, where there will be no need. As for not using a gland, this is also bad practice, unless the accessory is designed for the purpose, eg, some street lights.
 
agree^^^ best not to introduce joints if not necessary. but deffo use a gland. make sure SWA is well supported close to the CU so as not to put a strain on the box around the gland.
 
Try and fit a conduit box to the consumer unit,it can be fixed securely reducing strain on the cons unit and allow the termination of the Swa to be done

that is a good idea by des, and you can still use a banjo if you wish on the bush on the inside of thje CU. If it was a smaller cable, you could use the 4mm lug hole in the back of the box
 
Personally i would never convert a SWA cable to T&E in an adaptable box in this circumstance. If you mount the metal adaptable box directly under the CU enclosure connected via plastic or metal coupling or other, you can then make your SWA termination off with a banjo or earthing nut to the box and take your conductors straight through to the CU, ....Sorted!!


As stated above, introducing unnecessary joints is never a good idea, especially when talking about the larger sized of domestic cables.

I've never seen street lighting with a means of earthing SWA cables without making use of a gland, and can't picture them either. you can't clamp them, without putting undue stress on the internal conductors. If anyone has a link to these accessories, i'd be interested to have a look at them.... Some of the worst corrosion i've seen on SWA cables have been at street lighting positions...
 
Nothing stopping you from connecting the SWA cable off directly to the plastic CU enclosure using banjo's or earthing nut's either. So long as the cable is fully supported by correctly sized cable cleats....
 
Personally i would never convert a SWA cable to T&E in an adaptable box in this circumstance. If you mount the metal adaptable box directly under the CU enclosure connected via plastic or metal coupling or other, you can then make your SWA termination off with a banjo or earthing nut to the box and take your conductors straight through to the CU, ....Sorted!!


As stated above, introducing unnecessary joints is never a good idea, especially when talking about the larger sized of domestic cables.

I've never seen street lighting with a means of earthing SWA cables without making use of a gland, and can't picture them either. you can't clamp them, without putting undue stress on the internal conductors. If anyone has a link to these accessories, i'd be interested to have a look at them.... Some of the worst corrosion i've seen on SWA cables have been at street lighting positions...

http://www.google.co.uk/url?sa=t&rc...peWdCQ&usg=AFQjCNHl3HQiAKlC_wWmKpiQT7tFuxDr6A

some of the cutouts( try the link above), come with a cone attached, and you then use a jubilee clip to terminate the armour. Ive not used them, but been on jobs where they have been used. I dont like them either, but i also hate the indoor type glands, and use CW or E1W all of the time.
 
Last edited:
E54, they are called CET glands and the SWA gets clamped up with built in jubilee clips. Have used them on pedestal boxes, feeder pillars etc and also lighting columns.
 
billyhas, you say the SWA will be in a partition wall at first fix, will the CU be mounted surface on the board afterwards, or will it be a flush fit?
 
http://www.google.co.uk/url?sa=t&rc...peWdCQ&usg=AFQjCNHl3HQiAKlC_wWmKpiQT7tFuxDr6A

some of the cutouts( try the link above), come with a cone attached, and you then use a jubilee clip to terminate the armour. Ive not used them, but been on jobs where they have been used. I dont like them either, but i also hate the indoor type glands, and use CW or E1W all of the time.


Thanks johnboy, Yes i can understand what your talking about now!! lol! Think i would use a length of heatshrink, over a termination such as this. Don't think a normal shroud would suffice in conditions such as street lighting poles, which always tend to be damp in my experience...
 
Last edited by a moderator:
I never intended to join the cable. I just need to terminate through the back of a plastic consumer unit

Good to hear Billy, ..unnecessary joints are bad news at the best of times... I think you have more than enough acceptable alternatives now, on the best ways of how to terminate a SWA cable into your CU, so go get-um...lol!!
 
If you are planning to terminate through the back of the CU, I hope the stud wall is "thick" otherwise you'll have a devil of a job putting the correct radius/bend on the SWA even before you allow for the gland etc.
 
terminate into metal adaptable box, fixed flush into the stud wall with noginns top and bottom, leave the lid off and put the plasterboard on with the cables of your SWA coming through where you want, then you can surface mount the CU using the noggins top and bottom of the A/B as fixing points. simples
 
terminate into metal adaptable box, fixed flush into the stud wall with noginns top and bottom, leave the lid off and put the plasterboard on with the cables of your SWA coming through where you want, then you can surface mount the CU using the noggins top and bottom of the A/B as fixing points. simples

sounds like a PLAN. funny how it's only in post #25 that we find out he wants to come into the BACK of the CU!
 
sounds like a PLAN. funny how it's only in post #25 that we find out he wants to come into the BACK of the CU!
I apologise if there was any confusion but surely post #12 gave the info you thought was omitted until post #25.Please keep up
 
Last edited by a moderator:
OK, got me there. i must have missed that 2 liner while scrolling through the posts. then jase seems to have the easiest solution.
 
terminate into metal adaptable box, fixed flush into the stud wall with noginns top and bottom, leave the lid off and put the plasterboard on with the cables of your SWA coming through where you want, then you can surface mount the CU using the noggins top and bottom of the A/B as fixing points. simples

Cheers jase,should've thought of this myself
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
SWA submain into plastic consumer unit?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
31
Unsolved
--

Advert

Thread statistics

Created
BillyH,
Last reply from
BillyH,
Replies
31
Views
24,220

Advert

Back
Top