Thank you one and all, response has been great. Thanks you sir's. If in doubt type cyber call a Qualified Electrician.lol
Its obvious circuit and loading design have never been calculated here, your best bet here would be to replace the 1ph sub mains with a 3ph board and new 4core armoured off a triple pole 50amp mcb. this as well as balancing your loads over the phases will give you 150amp of 1ph availaility at submans. Loading calcs etc on existing 3ph board will be required to be worked out, who ever expected connecting several heaters + lighting circuits, sockets etc etc in a church on 1ph when 3ph available is a muppet and should stick to houses as i suspect is there background, no offense to the domestic installers but seems this system has been fitted by someone who has little or no experience of large buildings and or 3ph systems.
Partially my idea was to give the OP an idea here of how deep the water is hes stood in, seeing a more indepth reply will then allow him to conclude whether hes out of his depth or not, short quick although helpful answers can give OP a over confidence view of his problem where as a deeper explanation 'well in this particular case' will benefit the OP more, if he follows and understands my points then he can use them to rectify his problem, if hes getting confused with it all i believe he needs to seek onsite guidence from someone with more experience if not pass the job on.This is along the lines of what i might of posted but this may have thrown the op completely,but typical of these types of installation and agree with all said.
OP will need to be experienced in circuit loading and design if upgrading as suggested as replacing 1ph with 3ph will require a full inspection of all circuits on the 1ph board so as to balance them correctly, note for 400 volts that may become present in switching thus needing warning labels and 400v between adjacent points. What at first might seem like a board and cable upgrade may turn out to be alot more, balancing loads can reduce power consumption and running costs and may need to be calculated to justify the powers who be about the initial cost of rectifying someone elses mess, although not knowing the details of the job i suspect a few more heaters in use plus maybe heavy lighting load which should in this situe be balanced over 3 phases.
If you re-read the OP you should be aware hes guessing the swa is 25mm to 1ph board, im assuming here its not next door to 3ph board so would need to be fused less than 100amps, common rating 80amps possibly suffice, but he mentions 50amp MCB single pole within 3ph board so as most boards have max mcb ratings of either 50amp or 63amp he will still be too small, he mentions it trips approx 20mins after heaters switched on this would equate to about 75amps on time/current graphs so not really an option to upgrade. Its poor design at the least to have a single phase board loaded up that much when 3phase available and bad design as its tripping it own front end mcb, and this situe should be rectified and in light of the above - the best option is 3ph supply and 3ph board this will balance the 3phase loading reduce the electric bills and justify paying the tarriff to have 3 ph, if as you suggest other phases may be loaded up similar then this would mean a phase per area of church on single phase boards, again poor design as if only using one area of church than you phases are heavily out of balance and costly to the customer in unnecessary electric cost.can still keep the single phase board fed of the 3 phase, as long as you uprate the MCB and check the cable can handle the load, as for balancing the load across the phases, well that 1ph board just acts as 1 load on one phase so you would want to check the other loads on that 3ph board