Hello first post on here and been searching to see if they was a post like this online.
In a church building, there is a 3 phase board that feeds a wylex single phase ccu with a swa cable 3 core but not sure on size, my best bet is it looks like a 25mm. This single phase board is protected by a mcb 50A within the 3 phase board. Now the single phase board is a spilt load ccu. The main breaker for the single phase ccu is 100A, with two rcd rated at 80ma standard on most ccu. looks like a twelve way board. Now here is the problem. From that single phase board are two radial circuits 32A 4MM s.w.a 4 core, and everytime we plug in 3 pin heaters on the two circuits within 30mins or sometimes 1 hour (varies) it trips out the 50a mcb at the 3 phase board, which means it bypasses the 32a mcb on the single phase,main switch and rcd altogether. Whatsup with that.
At first I thought it was overload but did the formula to find that a 32A circuit can take about 7200 watts, 3 heaters on one circuit each about 2kw.So that ruled out overload, I don't think its a short because of the duration the circuit stays on for before it trips. I was hoping it was the way that they used one s.w.a 4 core to wire 2 radial circuits(shared neutral) basically instead of using a 5 core or running two sepaerate cables back to the board its just the one.But still trips 50A breaker.
I don't really know anything else about the circuit like supply type, but could find out if you have any ideas. Discrimination comes to mind about way it doesn't trip the closet mcb(lowest)i.e 32 a breaker. But other than that I just don't know. Please if you have time remember to reply, we need the heating for the homeless, I am a Electrician struggling, asking my brothers and sisters in arms to shed some light. Thanks
I would be tempted to stic a clamp meter on and see what loads being drawn, and where from.. also im asuming where you put ,,, two rcd rated at 80ma,, you ment 80 amp and 30ma? but yer a clamp meter i think would be your best bet see at what current it trips and why straight away..
Hi,You said that it trips the 50amp breaker,so as said above clamp meter and see what is being drawn,even if the 32a dont trip,those circuits may well be fine but what else is being fed and used at the same time as those heaters ie the sub main wylex board that you are referring too,typical type of installation where things have been added on over the years and soon the sub main is overloaded.
Yeah that's what I mean't Edd cheers. Clamp meter, ahhh yes will use that as well should give a clear indication of loads being pulled. Loose connections makes sense could be where their reset the breaker every 20 times it tripped. 3 heaters at 2kw each on each circuit yes. But 6kw on one radial circuit and 6kw on the other radial circuit. How do you arrive at 52A?
6kw + 6kw +12kw 12000 divide by 230v = 52A so the total load of those 2 circuits is 52A, are they the only circuits on the board? you said the board was fed via a 50mcb, so the total load of those 2 circuits is pulling more than the what the whole board is rated at
Yes i can confirm circuits have been added, so basically if I measured the Amps travelling through the s.w.a from the 3p to 1phase board and say it measures 124 Amps that means either I will have to upgrade the main switch 100A because it always says not to exceed this as the max rating. Or change to a 3phase board, or change the 50A breaker for a 63A breaker to give the single phase board more power to cope with additions circuits
Ahh yes. Those two radials turned on together will pull 52A, 26A EACH.(52) half of what the whole single phase board is rated at 100a main switch right. So that leaves 12 other circuits on the same single phase board with about 50A to share between them, is that what your getting at. But then if it can't handle that much power why not keep out the 32A mcb.
I would check the loading firstly,that cable supplying the board maybe at its limit for ccc so without knowing the csa upgrading to a larger cb may not be the ideal option.
Yeah a bit, but your clearing it up. Basically those two radials are drawing to much power from the 50A MCB at the three phase board. But what I cant get my head around is why the mcb doesn't trip on overload. unless like stated before the whole board is overloaded when all circuits are up and running.
Its obvious circuit and loading design have never been calculated here, your best bet here would be to replace the 1ph sub mains with a 3ph board and new 4core armoured off a triple pole 50amp mcb. this as well as balancing your loads over the phases will give you 150amp of 1ph availaility at submans. Loading calcs etc on existing 3ph board will be required to be worked out, who ever expected connecting several heaters + lighting circuits, sockets etc etc in a church on 1ph when 3ph available is a muppet and should stick to houses as i suspect is there background, no offense to the domestic installers but seems this system has been fitted by someone who has little or no experience of large buildings and or 3ph systems.
This is along the lines of what i might of posted but this may have thrown the op completely,but typical of these types of installation and agree with all said.
Hi mate,
As the others have said you don't seem to understand the loading.
If you are pulling 26A on each radial (52A in total), the 32A MCB protecting each radial will not trip, as 26A is less than 32A, but the combined load of 52A is exceeding the 50A MCB supplying the 1PH DB, and as the others have said, that is without any additional loading on the submain by other circuits on the 1PH DB.
Darkwood is correct, it would have been better to try and balance the loads across all 3 phases, using a 3 phase submain and 3 phase remote DB, as well as the extra current capacity this option would have given.
OP will need to be experienced in circuit loading and design if upgrading as suggested as replacing 1ph with 3ph will require a full inspection of all circuits on the 1ph board so as to balance them correctly, note for 400 volts that may become present in switching thus needing warning labels and 400v between adjacent points. What at first might seem like a board and cable upgrade may turn out to be alot more, balancing loads can reduce power consumption and running costs and may need to be calculated to justify the powers who be about the initial cost of rectifying someone elses mess, although not knowing the details of the job i suspect a few more heaters in use plus maybe heavy lighting load which should in this situe be balanced over 3 phases.
I totaly missed out on the amount of heaters he was using,, on re reading it i still cant see it,,must be going blind or is that the beer!!!
Partially my idea was to give the OP an idea here of how deep the water is hes stood in, seeing a more indepth reply will then allow him to conclude whether hes out of his depth or not, short quick although helpful answers can give OP a over confidence view of his problem where as a deeper explanation 'well in this particular case' will benefit the OP more, if he follows and understands my points then he can use them to rectify his problem, if hes getting confused with it all i believe he needs to seek onsite guidence from someone with more experience if not pass the job on.
You are not wrong there, been there and done this on more than one occassion, the worst one I recall was a hairdressing salon, which had a 3phase supply DB, and SP submain/DB (very similar to this scenario), with the amount of additions and bodges that had been carried out over the years, it ended up a full re-wire/re-design, as this was the cheaper option by far.
I have been to a callout at a hotel some years ago,3 phase supply,added on over the years by unexperienced people,fire brigade out before me,melted dno fuse as 1 of the phases overloaded and it took years of abuse for it to melt,it can happen if the installtion is not designed,installed,tested and maintained correctly,i wonder when the last time that church had a EICR(periodic inspection in old money)carried out.
can still keep the single phase board fed of the 3 phase, as long as you uprate the MCB and check the cable can handle the load, as for balancing the load across the phases, well that 1ph board just acts as 1 load on one phase so you would want to check the other loads on that 3ph board
Seriously thank you all, I Understand the problem better now. Will inform the client of option A - 3p to feed 3p board,(Which I can't see them paying for since they not prepared to spend over £500 on materials. Or option B- upgrading the breaker, but first checking the ccc of the armoured cable before changing anything. Thanks again
If you re-read the OP you should be aware hes guessing the swa is 25mm to 1ph board, im assuming here its not next door to 3ph board so would need to be fused less than 100amps, common rating 80amps possibly suffice, but he mentions 50amp MCB single pole within 3ph board so as most boards have max mcb ratings of either 50amp or 63amp he will still be too small, he mentions it trips approx 20mins after heaters switched on this would equate to about 75amps on time/current graphs so not really an option to upgrade. Its poor design at the least to have a single phase board loaded up that much when 3phase available and bad design as its tripping it own front end mcb, and this situe should be rectified and in light of the above - the best option is 3ph supply and 3ph board this will balance the 3phase loading reduce the electric bills and justify paying the tarriff to have 3 ph, if as you suggest other phases may be loaded up similar then this would mean a phase per area of church on single phase boards, again poor design as if only using one area of church than you phases are heavily out of balance and costly to the customer in unnecessary electric cost.
Single phase ccu trips out 3 phase Board
Australia
Brace56,
Darkwood,