Currently has 6mm T&E feed from a 32A MCB
I need to replace the shower, but does my current setup need upgrading?
 
Need to know more details before I can help you.
Length of run, new shower size, where the cable is installed.
Rcd protection?

New shower 7.5kw
Run 10M
Cable run is under ground floor, all accessible from cellar.

Thanks @rich.250
 
7.5kw at 230v == about 32 amps, and as the shower aint gona run all day, im gona go out on a lim and say its fine with what you have discribed. BUT!!! you will need RCD protection, no ifs no buts an RCD is a must...
 
replacing shower on it's own . test the existing cable. if it is all sound, then no need to upgrade. RCD protection should be fitted , even if only a like for like replacement.
 
i don't think there is a reg. in BS7671 re. RCD on a like for like replacement. however, the manufacturers instructions usually specify RCD, so that means you fit one.
 
yer but im sure even if there aint no reg, if just replacing the shower it would make you sleep better at night :) and im sure you will be taking responsibility for the install so it should really need to comply..
 
well. i would fit RCD, even if it meant fitting a stand alone unit next to CU ( assuming CU was rewireable 3036 fuses)
 
Ps r u doing it? Have you got calibrated meter to check RCD. Test button does not confirm it works properly with vindication, I would want it tested. I've fitted a fair few off the shelf that are duds.

Dont make em like they used to. I prefer the house brick ones
 
Ps r u doing it? Have you got calibrated meter to check RCD. Test button does not confirm it works properly with vindication, I would want it tested. I've fitted a fair few off the shelf that are duds.

Dont make em like they used to. I prefer the house brick ones

I'd have to disagree with that statement, RCDs if anything, HAVE improved over the years. But nowhere near to the point i'd trust/rely on them as my main form of protection against earth faults, as i've often stated on TT threads here. They still have a long way to go in the reliability stakes... lol!!
 
You're allowed to disagree :86:

All I meant was, in my (not very) extensive research of trip times of 30mA RCDs, the oldest ones are without fail...faster.


As for reliability, I know not, i never fitted any so don't know if they were a bagg of ....nails off the shelf. Spose could/would have been!
 
You're allowed to disagree :86:

All I meant was, in my (not very) extensive research of trip times of 30mA RCDs, the oldest ones are without fail...faster.


As for reliability, I know not, i never fitted any so don't know if they were a bagg of ....nails off the shelf. Spose could/would have been!

You maybe right, but i wouldn't say that i've noticed that older RCD units being faster than the present day units. As far as i know, the same tripping and time requirements associated with 30mA RCD devices, have remained the same for many years now. Even then the accuracy isn't great!! lol!!
 
The older RCD units (not got an image or a BS number for them to hand - sorry!) seem to be capable of lasting the test of time longer that the newer stuff. Lack of routine testing on the newer ones may be a contributing factor, but so many failing even mechanical tests that I come across. It's a sorry state of affairs they are so bad, especially in relation to TT systems when they can be all the more important. But with supplementary bonding starting to become a thing of the past due to RCD's its only a matter of time before someone is killed (hopefully an MP! Ideally House of Commons, whack the lot of them in one go!) because of failing RCD's.
 
yer but im sure even if there aint no reg, if just replacing the shower it would make you sleep better at night :) and im sure you will be taking responsibility for the install so it should really need to comply..


While I would also be inclined to fit an RCD on a replacement as well....it's worth pointing out that just 4 years ago there was no requirement to RCD a shower at all....it could run straight off a 3036 fuse if you wanted......and everyone slept at night just fine.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
7.5kw shower
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
greasemonkey,
Last reply from
SPARTYKUS,
Replies
23
Views
10,417

Advert

Back
Top