Got to wire up 6 fluorescent lights over the next few days to 1 switch.
Is the easiest way as follows.

Feed from CU to switch

Feed from switch to lamp 1 then daisy chain from light 1 - 2, 2-3, 3-4, 4-5, 5-6?

Many Thanks

Simon
 
either that, or 3 plate it at first light.
 
Can you think of an easier way?
Is the total wattage within the limits of your switch and protective device?
 
I did MD using 7 x 36 x 1.8 / 230 = just under 2 amps.

Did not account for PF - using HF fittings.
 
Last edited by a moderator:
Why would you not go to the switch with the neutral i am currently at colege and they teached us how to take the neutral to the switch saying it is perfectly safe aslong as it does not exceed the switch rating you can get a lot of good switchs now that have a connection for the neutral at the back of the swtch. So i would take it to the swich as long as the florecent lights are the end of the line
 
whats this continuing obsession with neutrals at switches?.....is it in an enclosure: YES.....is it accessable: YES.....
 