B

Bradzz

Hi im looking for a list of Circuit Breaker short circuit capacity ratings, that i can stick into my BGB.
list required would be for all fuse types, from BS 3036 to BS88. old and new types protective devices.
icon14.png


Also is there such a thing as fuse wire sizes gauge card? if so can some one point me in the direction of obtaining one.
icon3.png


Cheers people.
icon6.png
 
Theres a post (sticky possibly) on here so do a search or two and see what you find.

Cheers Murdoch, i have had a good look but, still unable to locate one. I found one for BSEN 60898 breakers but its short, im looking for the range of protective devices.
 
BS7671:1992+A1:1994+A2:1997 533-01-04 A fuse shall preferably be of the cartridge type. Where a semi-enclosed fuse is selected, it shall be fitted with an element in accordance with the manufacturer's instructions if any. In the absence of such instructions, it shall be fitted with a single element of tinned copper wire of the appropriate diameter specified in Table 53 A.
TABLE 53A
Sizes of tinned copper wire for use in semi-enclosed fuses
[TABLE="class: MsoNormalTable"]
[TR]
[TD] Nominal current of fuse element (A)
[/TD]
[TD="width: 240"] Nominal diameter of wire (mm)
[/TD]
[/TR]
[TR]
[TD="width: 237"] 3
[/TD]
[TD="width: 240"] 0.15
[/TD]
[/TR]
[TR]
[TD="width: 237"] 5
[/TD]
[TD="width: 240"] 0.2
[/TD]
[/TR]
[TR]
[TD="width: 237"] 10
[/TD]
[TD="width: 240"] 0.35
[/TD]
[/TR]
[TR]
[TD="width: 237"] 15
[/TD]
[TD="width: 240"] 0.5
[/TD]
[/TR]
[TR]
[TD="width: 237"] 20
[/TD]
[TD="width: 240"] 0.6
[/TD]
[/TR]
[TR]
[TD="width: 237"] 25
[/TD]
[TD="width: 240"] 0.75
[/TD]
[/TR]
[TR]
[TD="width: 237"] 30
[/TD]
[TD="width: 240"] 0.85
[/TD]
[/TR]
[TR]
[TD="width: 237"] 45
[/TD]
[TD="width: 240"] 1.25
[/TD]
[/TR]
[TR]
[TD="width: 237"] 60
[/TD]
[TD="width: 240"] 1.53
[/TD]
[/TR]
[TR]
[TD="width: 237"] 80
[/TD]
[TD="width: 240"] 1.8
[/TD]
[/TR]
[TR]
[TD="width: 237"] 100
[/TD]
[TD="width: 240"] 2.0
[/TD]
[/TR]
[/TABLE]
 
BS7671:1992+A1:1994+A2:1997 533-01-04 A fuse shall preferably be of the cartridge type. Where a semi-enclosed fuse is selected, it shall be fitted with an element in accordance with the manufacturer's instructions if any. In the absence of such instructions, it shall be fitted with a single element of tinned copper wire of the appropriate diameter specified in Table 53 A.
TABLE 53A
Sizes of tinned copper wire for use in semi-enclosed fuses
[TABLE="class: MsoNormalTable"]
[TR]
[TD] Nominal current of fuse element (A)[/TD]
[TD] Nominal diameter of wire (mm)[/TD]
[/TR]
[TR]
[TD="width: 237"] 3[/TD]
[TD="width: 240"] 0.15[/TD]
[/TR]
[TR]
[TD="width: 237"] 5[/TD]
[TD="width: 240"] 0.2[/TD]
[/TR]
[TR]
[TD="width: 237"] 10[/TD]
[TD="width: 240"] 0.35[/TD]
[/TR]
[TR]
[TD="width: 237"] 15[/TD]
[TD="width: 240"] 0.5[/TD]
[/TR]
[TR]
[TD="width: 237"] 20[/TD]
[TD="width: 240"] 0.6[/TD]
[/TR]
[TR]
[TD="width: 237"] 25[/TD]
[TD="width: 240"] 0.75[/TD]
[/TR]
[TR]
[TD="width: 237"] 30[/TD]
[TD="width: 240"] 0.85[/TD]
[/TR]
[TR]
[TD="width: 237"] 45[/TD]
[TD="width: 240"] 1.25[/TD]
[/TR]
[TR]
[TD="width: 237"] 60[/TD]
[TD="width: 240"] 1.53[/TD]
[/TR]
[TR]
[TD="width: 237"] 80[/TD]
[TD="width: 240"] 1.8[/TD]
[/TR]
[TR]
[TD="width: 237"] 100[/TD]
[TD="width: 240"] 2.0[/TD]
[/TR]
[/TABLE]


well, that's buggered me up. my micrometer measures in thous' of an inch.can't do with these millionmetres
forum msays that's less than 6 characters. wish i could count like that.
 
Cheers MarkieSparkie, i have this Table, what im looking for is the rating, E.g. 1361 100A type II = 33KA .
But i require the total list for all protective fuses/Breakers.

Cheers people for the reponses.
 
Hi MarkieSparkie, I found something, sort of what im looking for it was in GN3 page 60, of the 2002 addition, but to all thanks for the HELP!!!!, lol
 

OFFICIAL SPONSORS

Back
Top