D
Davisonp
sounds like the client may have pressured the O/P into saving the install....and just upgrading the C/U and the height of points served etc to an acceptable level....
have you conducted any preliminary tests here?
i mean whats your Ze like..(definately the first thing you do upon pre-inspection)
you need to IR test the existing stuff (before dismantling the system)
an R1 R2 will tell you whats what as far as the CPCs are concerned.. (in fact method 2 would be a better way here)
preliminary testing will tell you lots about the install (as is)...and anything that will need sortin out (before you procede with the C/U change
it may be that you have a `shared neutral` here....if so then you will have RCD issues straight away....
The client has asked me to do a condition report, and asked me whether the house needs re-wiring. I have handed in the condition report and told them that the circuits attached to the newer consumer unit are in good condition (no shared neutrals, I did check) but I could not confirm the condition of the ring mains and boiler spur until I could get access to the circuit and run the tests. However, from a visual inspection of the cable, there are no obvious problems.
The problem is that with the old consumer unit (3 circuits remaining) having a main switch that only disconnects the live supply, and having no access to the cables without damaging the consumer unit, I cannot run any tests for shared neutrals without ripping the lid off the consumer unit, and then I have to change it anyway.
A Similar problem exists when testing from the back of a socket. I cannot test for shared neutrals, or IR between neutral and CPC, so all I can realistically do is end to end continuity and R1+R2 tests. If there are shared neutrals, it is only between these three circuits (downstairs ring, upstairs ring and boiler radial), so until the problems are traced, these circuits can be placed under the same RCD, thus solving the shared neutral problem temporarly.
I would be surprised if there was a shared neutral problem on the rings as the kitchen extension and lighting rewire has been wired correctly, so there are only these three circuits.
I am trying to get my head around the options for the socket move’s as it is a question that will come up very soon after the CU change.
It sounds like I should be preparing the client for a full or partial rewire when the sockets are moved.