Remember its not the incoming supply to the welder that caused the damage... if this was undersized wiring then as you rightly pointed out it would overheat the line wires and/or Neutral if it had one; the damage is caused by the lower voltage output circuit and high impedance or open circuit issues may see the currents upto 800amps -( welder and settings dependant) hijack any earth system if it can find a return circuit to its negative terminal hence any unrelated circuit could have been damaged regardless of them been enrgised or not. 10yrs ago we had to rewire a full trunking system in a factory because the stray est' 600amp current used the 10mm earth in a trunking which turned white hot and melted into all the other circuits, 24 X 3ph circuit melted and shorted into a clump with the earth, it was only when it blew the welder supply circuit that the current stopped but the damage had already been done by then.
darkwood
I learnt something new today, having nothing to do with welders in my job (i am off to google and learn more)
PS its a shot in the dark but ive seen what you found so many times because of my field of work and it would be my no'1 suspect but the only other suspect is a loose neutral usually supply end where circuit may take advantage of a N/E fault that may have existed in the circuit you found damaged, id be checking all N connections from the incomming to the local DB.
darkwood
Easy way to understand it is to look at the current path of the low voltage/high current secondary circuit of the welder, it has to go from positive through the weld back to negative, now because most welders benches and items they weld are metal and sat on the ground its can give rise to a potential dangerous situe, if you clamp the return cable to a girder instead of the job it will try find an alternative path to get to that clamp on the girder and because its sat on the ground the many parallel paths will exist from the motor on the turning bed if the job is sat on one to going through the local trunking/earthing system to get to the clamp on the girder and because of the high currents it does alot of damage, it is designed to melt steel and weld it after all, copper has a much lower melting point too :sick: than steel.
The fact the welder is powered from elsewhere really makes no difference. Welders (person) have a lovely habit of striking an arc whether they have a good earth return path to the set or not.
Electricity will take the path of least resistance, it may be longer but that’s the way it’s going to go. Go in to engineering place and you will see welders happily working away with the return clamp just resting on the bench. He’s got his sparkler going and couldn’t give a ---- there’s smoke coming out the light fitting, socket or anything else. (Tell them the kettles on fire you may get a response).
Just read the first couple of post and didn't bother with the rest, no offence lads. I would inspect the lot! As mentioned , alterations and additions. Go all the way back to Ib In rating factors, grouping ambient,.... Volt drop, max llength, etc, thermal constraints, pssc compliance. In the long run it'll save you time. And your reputation. If your fix doesnt work from guessing, you will lose out financially.
Loop3 .... already given likely causes further on, either loose main or sub neutral where existing loads have utilised a E/N fault as a return path or high current damage from welder secondary side, the OP's discription shows that issues with overheating lines hasn't occured but has been overheating on the earth alone, a full inspection will thus be recommended to ensure the integrity of all circuits hasn't been compromised which will cover all your points mentioned and further investigation with our suggestions in mind as to why the earth overheated on its own without tripping the circuit or showing heat damage to line conductors.
And who's going to pay for this? It is a farm!
Welder could be using the piller drill cpc as a earth return, I'm guessing they do some welding in a vise bolted to a steel bench which the drill is stood on?
PhilB,
electric will,