My mate asked me to look at his board as a funny smell was coming off it. Looked inside & the neutral going into the RCD was melted & so was the switch. It's a split load dual RCD board. The RCD switches are both rated 64A 30mA. My first thought was that it could have just been a loose neutral but then my second though was maybe the switch wasn't the correct rating. On othis side that the RCD protects he has two rings: one is the downstairs sockets & the other is the kitchen sockets, a 40A shower & a lighting circuit. I know these obviously ain't gonna be drawing their full loads at once but is it still too much?
 
Most likely a poor termination of wiring into the screw clamp of the RCD. I'm sure you'd have noticed most of the other usual suspects such as condensation, insects, debris ingress from drilling above etc. Some pics may confirm if you can upload a couple.
 
Could well be an over load. At one moment in time at lot of loads could have been running simultaneously. It wouldn't take long to over heat the conductors. then the damage just gets worse.
 
And it's always the neutral that's loose, I'm waiting for the definitive reason why it's always the neutral ;)
 
Check the resistance between the neutral bar for that RCD and the incomer. Would expect that to show a high reading, pointing to a loose terminal or a faulty RCD.
 
Lol they must be the ones that most people forget to tighten.
 
Last edited by a moderator:
Has all the signs of loose neutral and arcing over a long period of time,seen one recently,80A 30ma main switch,neutral wriggled out easily,so dont expect it was to correct torque,when i had recent assessment the inpsector checked my main switch terminations with his torque driver,spot on,and i dont have one,yet anyway but will get a set as quite handy.
 
And it's always the neutral that's loose, I'm waiting for the definitive reason why it's always the neutral ;)

I have the answer to that one.

It's the same as the Buttered side of toast / bread/ etc, landing on the floor more than the non buttered,, it doesn't.

You remember a neutral being loose, you don't remember the the Live being loose, or even the Earth, on average the same number of times.
 
seems to be a mindset problem with some sparks. tighten the L dog tight, coz it's the important one, but the N is just a return.
 
Sorry guys have no pictures as I just dumped it. I just replaced it like for like. I'll maybe upgrade it to the next size up though just to be sure...thanks for your help.
 