H
highspark
Call out - lighting had fell into a fish tank whilst guy was on holiday.
He returns to a load of dead fish and no power.
RCD is main switch protecting whole house.
With all circuit breakers down... RCD still wont switch back on.
So disconnected fish tank from mains. RCD still wont switch on.
Disconnect RCD from everything switch now reinstates itself.
Switch everything on 1 by 1. Lights ok up and down... Alarm ok. Down sockets trip. Up sockets trip. Kitchen sockets trip. Cooker ok, Garage trip.
Without doing anything else but putting the front cover back switching MCB's on one at a time and then switching RCD on afterward the RCD holds and seems to be working fine.
Madness and not ghe first time its happened to me... Bloody RCD's
Had a case were cable to fish tank had tracked water from fish tank to socket and soaked it worth a check
Did you actually test the RCD on times half, one and five at nought and one hundred and eighty degrees to determine whether it is faulty or not, jeez.
the only concrete thing here is that it takes <30mA to kill fish.
As MDJ said, RCD test everything - that will determine whether uve got a faulty RCD or not. If not, you'll have to get your fault-finding head on :biggrin5:
Sounds like a neutral to earth fault so when you are energising socket circuits with some load on its taking out rcd, did you check for neutral to earth fault?
All tests fine. Done ramp and trip times before I left
Couldnt do any RCD tests at first becuse it wouldnt switch up...
Madness!
Yep my thoughts exactly. He needs to separate them neutrals and check them with an insulation resistance tester. Could be an old RCD which has the tripping mechanism ceased and the strength of the fish tank fault has now freed it up hence can now operate as it should.
Has to be all neutrals out then back one at a time and try to reset. After that it has to be the rcd.
You heat up a fish, I find it tends to kill it fairly quickly.
Perhaps my fryer is set too high?
If I were Inspector Morse, or Poirot, I'd be looking for a cat.
Perhaps one of the neighbours has a cat?