Call out - lighting had fell into a fish tank whilst guy was on holiday.
He returns to a load of dead fish and no power.
RCD is main switch protecting whole house.
With all circuit breakers down... RCD still wont switch back on.
So disconnected fish tank from mains. RCD still wont switch on.
Disconnect RCD from everything switch now reinstates itself.
Switch everything on 1 by 1. Lights ok up and down... Alarm ok. Down sockets trip. Up sockets trip. Kitchen sockets trip. Cooker ok, Garage trip.
Without doing anything else but putting the front cover back switching MCB's on one at a time and then switching RCD on afterward the RCD holds and seems to be working fine.
Madness and not ghe first time its happened to me... Bloody RCD's
Did you actually test the RCD on times half, one and five at nought and one hundred and eighty degrees to determine whether it is faulty or not, jeez.
the only concrete thing here is that it takes <30mA to kill fish.
As MDJ said, RCD test everything - that will determine whether uve got a faulty RCD or not. If not, you'll have to get your fault-finding head on :biggrin5:
All tests fine. Done ramp and trip times before I left
Couldnt do any RCD tests at first becuse it wouldnt switch up...
Madness!
Sounds like a neutral to earth fault so when you are energising socket circuits with some load on its taking out rcd, did you check for neutral to earth fault?
Yep my thoughts exactly. He needs to separate them neutrals and check them with an insulation resistance tester. Could be an old RCD which has the tripping mechanism ceased and the strength of the fish tank fault has now freed it up hence can now operate as it should.
If it was a tropical fish tank the fish probably died from lack of heating as well as lack of oxygen from the pump!! Or unless equiped with an auto feeder, starved to death... lol!!
Reply to RCD - anyone had this in the UK Electrical Forum area at ElectriciansForums.net
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
7K