Stuuk1

Hi all,

The old shower isolator was in the airing cupboard, is it acceptable to fit my new isolator in the same cupboard?

The cupboard is an airing cupboard on the landing just outside the bathroom.

Or does the isolator need to be inside or just outside the bathroom by the fan isolator?

Thanks
 
if it's a wall switch it needs to be outside the bathroom. in the cupboard is fine, --- uming the door to the cupboard opens onto the landing.
 
I think you would be ok to replace the existing isolator in the same position, you don't want that big thing on show (ooer).
 
No problem mate ive put them there loads of times if customer does not want it in bathroom ,dont use cord switch though use 45a plate switch(cooker type)
neil
 
Thanks so much!

I was expecting a torrent of abuse for asking that haha,but better to ask than to get it wrong...

I'm glad that it can go in the cupboard because I've made all the walls good and then the plumber advised to put an electric shower in rather than a mixer due to the new combi boiler.

Thanks again, you lot are stars! Stay tuned for another of my questions very shortly in a separate thread about cooker points... ;)
 
I was expecting a torrent of abuse for asking that

Nothing wrong with the question, but you may have opened the can yet, I feel the questions about single pole and double pole isolation and MCBs will be adequate for isolation coming lol
 
I'm certain that if you really find the lack of abuse to be a problem, that someone wil oblige shortly.
 
Did the shower have an integral means of switching off? I assume so, in which case the isolator wasn't even needed (that's not to say that ommision is a good idea), so in the landing cupboard is fine.
 
Did the shower have an integral means of switching off? I assume so, in which case the isolator wasn't even needed (that's not to say that ommision is a good idea), so in the landing cupboard is fine.

Unless you read the manufacturers instructions which nearly always say double pole isolator.
 
Unless you read the manufacturers instructions which nearly always say double pole isolator.

No they don't, that's a rather uneducated assumption (no offence). Withouthttps://www.google.co.uk/search?hl=...a=X&ei=hn30UIm0DdDY0QXZhICwCQ&ved=0CDEQvwUoAA exaggeration I have fitted just about every make of shower available (we carry out a lot of work for a large local bathroom/wetroom specialist) and in my experience the showers that tend to ask for double pole isolation are the ones bought from the DIY sheds, higher spec and more specialist makes tend to have very little instruction.

Even then, the BGB only asks me to take account of manufacturers instructions, it doesn't say I MUST follow them.
 