I'd appreciate peoples views on this, including compliance or otherwise with the regs.

I've come across a 1-bed flat where one ring main serves the small kitchen, and boiler & security alarm. The unusual thing is that the ends of the ring are then connected to a single 6mm T&E that runs back to the consumer unit.

6mm is run through ceiling/floor void, holes in joists (no insulation), and down a steel conduit to the consumer unit.
6mm Run length is 20m max and it's protected with a 32A MCB.

Kitchen is being refurbed, and the run back to the consumer unit is really difficult to access, so question 1 is, does the existing arrangement comply with regs?

Question 2. There is also a single 2.5mm radial from the consumer unit (16A MCB) to the Kitchen area (was an old storage heater I believe). Cable is run the same way as above.
Is this likely to be sufficient if they install a simple 600mm wide built-under oven and electric hob?
What about changing the MCB to 20A?
I guess the hob could be powered from the above "ring" if necessary.

Any thoughts?
Thanks.
 
Hi

In my opinion

The ring connected to the 6mm feed is a non standard final circuit but I wouldnt see an issue with it as long as the the Zs does not exceed the maximum stated for a 32A MCB and of course that your r1, rn and r2 values are good.

The single oven will be 13A Max and can be fed via a standard 13A Plug or fused spur from the 20A Supply under the cabinets
 
Re: Using a 6mm T&E to feed a Ring Main

Only you know by designing the circuits with the loads expected..

was at job last wek where the guy spur'd of ring in 4mm for 3 extra sockets, he said its covered by breaker do dead on.. Where I would of put spur in and then added 3 skts..

- - - Updated - - -

Lollipop
 
Its often referred to as a lollipop circuit, not that you would find it in a regs book.

Sometimes its the only way to work and thats to "adapt" a redundant cooker ciruit so if the dead readings are good and under the max for the MCB whats the issue - except how do you fill out the EIC?
 
As far as point 1 is concerned, it is not a conventional circuit arrangement as set out by BS7671, However, this is what is commonly known as a Lollipop circuit and is safe. The 6mm2 is protected by the CPD you state. As long as the connection with the ring legs is accessible, the end to end readings of the ring portion are integral and the Zs values comply then electrically there is no adverse or unsafe conditions to note.

Point 2 You need to ascertain the characteristics of the oven you tend to install via this circuit. Generally if it is fan assisted you will find it comes with a plug top which means your circuit will be ok to use with a 20A MCB as these tend to be rated at around 2.4 kw.
If a conventional oven is to be placed you need to look into the possibility of a 32A 6mm2 circuit to cope with approx 5KW.
 
Re: Using a 6mm T&E to feed a Ring Main

The RFC on the 6mm is as Llandrillo said, non standard BUT was commonly used once upon a time and is known as a lollipop ring. As long as all cables involved in this non standard arrangement have adequate ccc and as long as all disconnection times can be met then I see no problem with it. The changing of the 16A MCB on the radial to a 20A only you can answer that one mate as you're the one who knows the likely load on that cable.

- - - Updated - - -

Edit, Beaten to it by just about everybody:)
 
Re: Using a 6mm T&E to feed a Ring Main

i have used 4mm t&e for the first and last legs on a large ring to help with volt drop if the sockets are a long way from the db
the joints are accessable as they are made in the socket outlets
 
Is this likely to be sufficient if they install a simple 600mm wide built-under oven and electric hob?
What about changing the MCB to 20A?
I guess the hob could be powered from the above "ring" if necessary.

Don't think I would be supplying an electric hob from a ring circuit.
 
But there isn't going to be a reduction in the current capacity is there? 1 x 6mm = 32A, 2 x 2.5mm = 32A

Just saying. lol

Doh, didn't think of it in that way, just in the reduction in cable size. 2nd time I've felt like a muppet this week :frown2:
 