E
Engineer54
Question 2. There is also a single 2.5mm radial from the consumer unit (16A MCB) to the Kitchen area (was an old storage heater I believe). Cable is run the same way as above.
Is this likely to be sufficient if they install a simple 600mm wide built-under oven and electric hob?
What about changing the MCB to 20A?
Any thoughts?
Thanks.
There is no-way a 16A or 20A radial circuit on 2.5mm T&E will cope with both an oven and a hob!! So you had best get a 6mm cable in while you can, to supply these two cooking appliances!!