Just to pick up on the point raised earlier, regarding spurring off a ring in 4mm to feed more than one socket outlet. I can kind of see the logic in that, and have seen it done a couple of times. Was debating this with another spark ages ago, my argument about not doing this would be that although the 4mm is protected, the potential exists to overload one point of the ring. Thoughts?

Personally, I don't see it as good practice. Regardless of the conductor size, I'd always fuse down when supplying more than one socket.
 
I myself would use a spur as my interpretation of the regs was for a non fused spur direct of the ring was either one fixed 13A spur, 2 single sockets or one double socket. You can even use 1.5 T/E on the outlet connection of the fused spur to feed extra sockets BGB page425
 
Just to pick up on the point raised earlier, regarding spurring off a ring in 4mm to feed more than one socket outlet. I can kind of see the logic in that, and have seen it done a couple of times. Was debating this with another spark ages ago, my argument about not doing this would be that although the 4mm is protected, the potential exists to overload one point of the ring. Thoughts?

Personally, I don't see it as good practice. Regardless of the conductor size, I'd always fuse down when supplying more than one socket.

its bad practice , frowned upon , and risks unbalancing 1 of the ring legs if not branched off at the ring mid-point.
but i've done it a couple times myself cos it solved a big headache lol.
i wont bother with the tin hat as im passed giving a crap.
;-)
 
Hi, this came up in professional electrician a few months back - they referred to it as a 'hybrid ring circuit'. The outcome was that it was perfectly acceptable. Useful it rings are to be controlled via contractors (I.e emergency stops ect)
 
Question 2. There is also a single 2.5mm radial from the consumer unit (16A MCB) to the Kitchen area (was an old storage heater I believe). Cable is run the same way as above.
Is this likely to be sufficient if they install a simple 600mm wide built-under oven and electric hob?
What about changing the MCB to 20A?
Any thoughts?
Thanks.

There is no-way a 16A or 20A radial circuit on 2.5mm T&E will cope with both an oven and a hob!! So you had best get a 6mm cable in while you can, to supply these two cooking appliances!!
 
Hi, this came up in professional electrician a few months back - they referred to it as a 'hybrid ring circuit'. The outcome was that it was perfectly acceptable. Useful it rings are to be controlled via contractors (I.e emergency stops ect)

Any circuit that isn't classed as a standard circuit, is classified as a ''Hybrid''.... Lollipop rings have been around for donkey's years!! lol!!
 
Its often referred to as a lollipop circuit, not that you would find it in a regs book.

Sometimes its the only way to work and thats to "adapt" a redundant cooker ciruit so if the dead readings are good and under the max for the MCB whats the issue - except how do you fill out the EIC?
............
 
Hi, this came up in professional electrician a few months back - they referred to it as a 'hybrid ring circuit'. The outcome was that it was perfectly acceptable. Useful it rings are to be controlled via contractors (I.e emergency stops ect)

I was about to post this, glad I read the whole thing before I did
 