Doh, didn't think of it in that way, just in the reduction in cable size. 2nd time I've felt like a muppet this week :frown2:
Not a muppet mate, this is what the forum is for!
Doh, didn't think of it in that way, just in the reduction in cable size. 2nd time I've felt like a muppet this week :frown2:
Just to pick up on the point raised earlier, regarding spurring off a ring in 4mm to feed more than one socket outlet. I can kind of see the logic in that, and have seen it done a couple of times. Was debating this with another spark ages ago, my argument about not doing this would be that although the 4mm is protected, the potential exists to overload one point of the ring. Thoughts?
Personally, I don't see it as good practice. Regardless of the conductor size, I'd always fuse down when supplying more than one socket.
Question 2. There is also a single 2.5mm radial from the consumer unit (16A MCB) to the Kitchen area (was an old storage heater I believe). Cable is run the same way as above.
Is this likely to be sufficient if they install a simple 600mm wide built-under oven and electric hob?
What about changing the MCB to 20A?
Any thoughts?
Thanks.
Hi, this came up in professional electrician a few months back - they referred to it as a 'hybrid ring circuit'. The outcome was that it was perfectly acceptable. Useful it rings are to be controlled via contractors (I.e emergency stops ect)
............Its often referred to as a lollipop circuit, not that you would find it in a regs book.
Sometimes its the only way to work and thats to "adapt" a redundant cooker ciruit so if the dead readings are good and under the max for the MCB whats the issue - except how do you fill out the EIC?
Hi, this came up in professional electrician a few months back - they referred to it as a 'hybrid ring circuit'. The outcome was that it was perfectly acceptable. Useful it rings are to be controlled via contractors (I.e emergency stops ect)