For a board installation :confused: In the 'Merry Old Land of Oz' maybe, but not here.
Everyone Ive ever spoken to in the industry outside the NIC has maintained a cu change should be a periodic (EICR now) not an EIC I remember being told this at college and also when I did 2391, personally I think either is ok, I don't have the regs in front of me but if memory serves they say something like "suitable certificates should be filled prepared"
Sorry odawire, but CU change is EIC. Not sure what publications you're reading...
I agree with you, but after having this discussion many times with people over the years I've never heard anyone really give a good reason why, the only argument I can really give is beacause im changing the protective device it should be EIC, I'd love if you could clear this up with something from bs7671
Surely the clue is in what the acronyms EIC and EICR actually stand for. The clue is right there is it not? Daz
The new cu is being installed, but the wiring is not, I guy from the EIT told me you should do both! That seems a bit melodramatic to me, also its notifiable work so that's another argument for the EIC
If your are installing a new consumer unit then the certification that is required for that job is an Electrical installation certificate.
The process of changing a consumer unit can be fraught with problems because of the state of the attached circuits (as you have found) therefore the ideal situation is to do an EICR on the installation before changing the consumer unit in order to identify any problems. Since most customers will not pay for this the reality is that at least some basic checks will be carried out to identify major problems (usually without any sort of certificate going to the customer but the electrician should record the values).
Advice can then be given to the customer about further work required before the Consumer unit is changed, this allows the electrician and/or customer to decide not to go ahead if they wish and gives full transparency of the process.
Once the Consumer change is agreed the electrician can undertake the work, and then complete an electrical installation certificate for the change (possibly using some of the values obtained from earlier testing where no changes have been made (although the protective devices will have changed)).
And then notify building control through his scheme.
Agreed
Changing a CU alters the characteristics of the installation, therefore some form of installation certificate should be issued. It's not a minor works, so it must be an Electrical Installation Certificate ( the clue's in the middle word). You're not reporting on the condition, you're certifying your installation.
Is it not right to do an EIC for the CU change and an EICR for the testing and inspection afterwards? Also if IR test is 7MΩ, it shouldn't be tripping should it?
No, you don't do an EIC and an EICR. You test the circuits before reconnecting to the new CU, and note the readings on the certificate. If they are non-compliant they should not be reconnected.
That said, if you have been asked to carry out an EICR in addition, then there's nothing wrong with that, but it will be a lot more in-depth.
I do basically agree with what your saying, but the problem is that an EIC does not account for anything outside 17th edition, which just isn't realistic, there must be situations where the CCU is changed but NCS cabling is connected.
Even though everyone you've ever spoken to outside the NIC has told you that it should be an EICR?
You are confusing me now...
I never said those people were right, was just explaining my experience, Part P wants an EIC but BS7671 wants a EICR, as I said before either one is acceptable in my opinion.
Could you tell me where BS7671 states only an EICR is needed for a CU change please.
Good grief, is this thread the reincarnation of 2391? :)
GN3 to the ready, chaps.
Its more what it doesn't say, EIC is required for a new installation or changes to an existing installation. It depends how you want to view a CCU change, If your not changing any fixed wiring or maybe just adding RCDs in which case you may not even be changing the protective device. And there are a lot of different opinion's on this, but obviously not on this forum
Right, you've answered your own question there so that's sorted at last. What are you going to do about the RCD issue then? Daz
EIC required. Can't imagine how anyone could understand otherwise??
Apart from a full rewire, a change of CU is probably the most onerous change to an installation you can make, to suggest that what certification you decide to use is down to interpretation is, frankly, ridiculous.
I would bet my house that if you went on the IET forum and postulated the same belief's you have here, you would be shot down just as quickly.
However, if you feel strongly about it, may I suggest you use an EICR for your board change and then use that same installation as one of the ones that gets inspected for your annual scam assessment.
As the others have said many times now, it's not open to interpretation at all. A CU change is definitely a change to an installation and not open to debate. You will also find it stated in many publications that it requires an EIC.
All the people you have spoken to over the years regarding this matter are simply wrong if they have told you that an EICR is acceptable. Have you personally changed a CU and not issued an EIC by any chance?
As you are changing the CU, you are obviously with a part P scheme. Give them a ring and see what answer you get. :)
I would bet my house that if you went on the IET forum and postulated the same belief's you have here, would be shot down just as quickly.
If you read the thread you can see I don't feel strongly about it, Its something I agree with you guys on lol, what im saying is many of people I have talked to over the years have stayed strong with the idea of PIR for a CU change most of them interestingly enough from the IET, and your gonna have to explain that last sentence to me please as I don't like the sound of it
- - - Updated - - -
Yes I agree
On this forum, members generally refer to the different part p schemes as 'scams', in reference to the fact they do bugger all for your money and are simply contributing to an overall malaise in the electrical industry.
What I was saying in my last sentence was that if you feel that an EICR is acceptable paperwork for a CU change then use that same piece of work as one of the one's that you have your annual assessment done on. The implication being that you will get a -------ing from your scheme (scam :smilewinkgrin:) assessor.
Cheers
Cheers
Ok sorry, thought you were being out of order
No problem, and no apologies necessary.
Nothing on here really get's personal, apart from a few idiots who don't last long anyway, but you will find lots of peeps with forthright views who will defend them vigorously. Obviously sometimes 'vigorously' can get a little OTT.
Cheers
Ok, so apart from the disagreements on what's right and wrong and what certificates are needed, which has definitely been dealt with, I think everyone has missed an important point,
Hi, should have explained, I have a rig I made up I use sometimes, its basically an rcd adaptor that I wire into and plug into a socket, when I did this it tripped
firstly, you've done IR tests and you know that whatever is wrong with the circuit, the readings calculate out to an acceptable value, so end of you should be happy to connect this to an Rcd. but you are relying on a home brewed tester to test whether its safe to connect to Rcd, I would look here for your answer. Your calibrated tester is telling you everything you need to know
Its not something I use a lot, its just been handy a few times
Reply to Departures from bs7671, certification. in the UK Electrical Forum area at ElectriciansForums.net
Eh up :) I've done some new PDF forms for BS7671 18th Edition Amendment 2 2022 (the Big Brown Book), based on the IET model forms. You can fill...
12K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
8K