Hi, I have always made sure my installs have no departures from bs7671 but I'm doing a ccu change next week and have done some preliminary testing and the heating circuit (boiler and heating controls) has low IR readings, had a look in all obvious places and cant find any problems, had trouble breaking the circuit up as its a bit messy, client has just decorated so he doesn't want any damage to the house, seeing as its all fixed equipment (I'm unsure on the cable routes but id guess its buried less than 50mm at some point) is it acceptable to leave this circuit unprotected and note it on the departures section? all the earthing/bonding is mustard. Any experience on this would be appreciated, thanks.
 
Mate you have asked a question and been given the correct guidance by different members. Just because you may not like what you hear is not the fault of the forum.

Its not that I don't like what I hear, I don't know why people are talking about me being in court when all I did was pose a hypothetical question, there's a tendency for people on this forum to assume that your totally stupid and don't have a clue what your talking about and I find that a bit ridiculous, I wonder if some of these people have conversations like this in real life?
 
A few questions:
Is there a fault on the circuit in question?
Do you intend putting this circuit on the non-RCD side because it will trip if you put it on the protected side?
Would you say a faulty circuit counts as a 'Departure from bs7671 regulations'? (quoted from your thread title)

Be interested to see some YES/NO answers for these, rather than waffle.

It seems you are looking for a reg you can use to justify this, when the real issue is the fact that you have a faulty circuit. Daz
 
A few questions:
Is there a fault on the circuit in question?
Do you intend putting this circuit on the non-RCD side because it will trip if you put it on the protected side?
Would you say a faulty circuit counts as a 'Departure from bs7671 regulations'? (quoted from your thread title)

Be interested to see some YES/NO answers for these, rather than waffle.

It seems you are looking for a reg you can use to justify this, when the real issue is the fact that you have a faulty circuit. Daz

Is there a fault on the circuit? Yes

Do I intend to put on non-rcd side? No but I was interested to hear peoples thoughts as it seems unclear.

Would I say a faulty circuit is a departue? Possibly yes, posibly no, don't have enough information yet.

I'm not looking for a reg to justify and I'm not waffling
 
Right, so you don't intend to put it on the non-RCD side. In that case you will be putting it on the RCD side. In which case, the fault will need fixing.

Daz
 
In one part of the document it says rcd protection should be required for buried cables, but in another part (and in the regs) it says C3 can be connected to a new CCU, that is a contradiction.


1.No where in the regs does it say that it can be a C3 on a EICR

2. You will be filling in a EIC not a EICR so that totally contradicts what you are saying.
 
1.No where in the regs does it say that it can be a C3 on a EICR

2. You will be filling in a EIC not a EICR so that totally contradicts what you are saying.

I'm refering to it as a C3 (quicker to write) code as it says a fault not causing an imeadiate danger, and thankyou I'm well aware of what certificate I need to fill out, however an EICR is acceptable for a fuseboard change, but NIC says EIC and that's the only reason I do an EIC, BS7671 asks for a EICR.
 
I'm refering to it as a C3 (quicker to write) code as it says a fault not causing an imeadiate danger, and thankyou I'm well aware of what certificate I need to fill out, however an EICR is acceptable for a fuseboard change, but NIC says EIC and that's the only reason I do an EIC, BS7671 asks for a EICR.

It's irrelevant what the NICEIC say. A CU change generates an EIC.
 
For a board installation :confused: In the 'Merry Old Land of Oz' maybe, but not here.

Everyone Ive ever spoken to in the industry outside the NIC has maintained a cu change should be a periodic (EICR now) not an EIC I remember being told this at college and also when I did 2391, personally I think either is ok, I don't have the regs in front of me but if memory serves they say something like "suitable certificates should be filled prepared"
 
Sorry odawire, but CU change is EIC. Not sure what publications you're reading...

I agree with you, but after having this discussion many times with people over the years I've never heard anyone really give a good reason why, the only argument I can really give is beacause im changing the protective device it should be EIC, I'd love if you could clear this up with something from bs7671
 
Surely the clue is in what the acronyms EIC and EICR actually stand for. The clue is right there is it not? Daz
 
If your are installing a new consumer unit then the certification that is required for that job is an Electrical installation certificate.

The process of changing a consumer unit can be fraught with problems because of the state of the attached circuits (as you have found) therefore the ideal situation is to do an EICR on the installation before changing the consumer unit in order to identify any problems. Since most customers will not pay for this the reality is that at least some basic checks will be carried out to identify major problems (usually without any sort of certificate going to the customer but the electrician should record the values).

Advice can then be given to the customer about further work required before the Consumer unit is changed, this allows the electrician and/or customer to decide not to go ahead if they wish and gives full transparency of the process.

Once the Consumer change is agreed the electrician can undertake the work, and then complete an electrical installation certificate for the change (possibly using some of the values obtained from earlier testing where no changes have been made (although the protective devices will have changed)).
And then notify building control through his scheme.
 
If your are installing a new consumer unit then the certification that is required for that job is an Electrical installation certificate.

The process of changing a consumer unit can be fraught with problems because of the state of the attached circuits (as you have found) therefore the ideal situation is to do an EICR on the installation before changing the consumer unit in order to identify any problems. Since most customers will not pay for this the reality is that at least some basic checks will be carried out to identify major problems (usually without any sort of certificate going to the customer but the electrician should record the values).

Advice can then be given to the customer about further work required before the Consumer unit is changed, this allows the electrician and/or customer to decide not to go ahead if they wish and gives full transparency of the process.

Once the Consumer change is agreed the electrician can undertake the work, and then complete an electrical installation certificate for the change (possibly using some of the values obtained from earlier testing where no changes have been made (although the protective devices will have changed)).
And then notify building control through his scheme.

Agreed
 
Changing a CU alters the characteristics of the installation, therefore some form of installation certificate should be issued. It's not a minor works, so it must be an Electrical Installation Certificate ( the clue's in the middle word). You're not reporting on the condition, you're certifying your installation.
 

Reply to Departures from bs7671, certification. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock