Hi, anyone got any advice re this problem that I can't solve....
I have 2 PV arrays installed, a 4.2Kw and a 5.0Kw. The electricity supplier here made me install them on 2 seperate single phase supplies. My house now runs on 2 seperate supplies, half on one supply and the other half on the other.
My house is 80m from the main road so the electricity meters are at the roadside and then two 35mm2 cables run up to the house.
At the road end each supply has a seperate board with a 50amp mcb and a 300ma RCD. At the house end each supply has its own board with 30ma RCD's.
The PV arrays are connected into the house end of the 35mm2 cables, without going through any of the house boards. Each array has its own mcb and 30ma RCD on its feed out to the cable.
The problem is that overnight I keep getting random trips of the 300maRCD's at the road side. I think it happens when it gets light and the panels start to generate. It happens about every 3 or 4 days and is not the same RCD each time. Is this something to do with reverse flow?
Any one got any ideas as to what is going on?
Make sure the 300m/A rcd is correct type, I think you need a type A and not a type AC, you may have to do some research, to find the right one for your application.
that's bizzare, it shouldn't be tripping out a 300mA RCD.
what inverters and panels do you have, and what roof construction is it?
The issue will be something to do with capacitance, which occurs most in damp conditions on TL inverters, but it really shouldn't be tripping out a 300mA RCD - for reference, we install most of our 3.7kW limited TL inverters on 30mA RCDs on dedicated circuits and have never had a tripping issue other than in the event of a grid fault. Manufacturers recommend 100mA, so 300mA per inverter should be more than adequate.
unless of course you've already for some significant earth leakage going on. Do you have any other circuits not on the 30mA RCDs in the house that could be responsible for live neutral imbalances on both sides? maybe a rogue shared neutral / neutral > shared earth fault > neutral on something like a heating circuit that also comes on at that sort of time? Maybe try switching the solar off over night and see if it happens without it just to be sure?
Hi, thank you for that. I have Sunny inverters a 4kw and a 5kw. The only other load I could think was a 1kw dehumifier (because we have building work going on), but I turned this off and the tripping still happens.
I have been starting to wonder whether the problem is to do with the earth. Earthing is by a two 2.5m copper rods driven into the ground vertically. One is next to the meters, th eother inside the house at the other end of the 35mm2 cable. Both supplies share th esame earth as the 35mms cable is actually a 4core 35mm2 swa.
I have been 'googleing' and still can't find the answer. However, the Americans seem to get quite concered with revers feed and make sure that they have RCD's that are reverse flow compatible. Has anyone come across this?
sounds like it could also be inductance in the cable?
What loads are you running overnight? Any electric heating, storage heaters or other big loads?
Reply to PV Array trips RCD's in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...