Discuss Faulty RCD tripping on the button but not via the tester in the UK Electrical Forum area at ElectriciansForums.net

Have a thorough read through the thread I've linked below Tony. I had a similar problem to you (ignore the fact I wrote that the RCD was faulty in my first post in the linked thread, I was wrong as I suspect you may be) and this thread helped me to understand why a perfectly good RCD will not trip when tested from a socket or light rather than at the RCD itself (with outgoing terminals disconnected).

It is always unlikely that the RCD is faulty, not impossible, just unlikely. I have only come across a handful of faulty RCD's in the last 10 years.

Here is the link/thread Why isnt the RCD tripping? - https://www.electriciansforums.net/threads/why-isnt-the-rcd-tripping.176881/#gsc.tab=0
Will do thanks.
 
RCD's sometimes seemingly dont operate within the specfied time when tested with loads in circuit because of an appliance with a capacitor. Fridges and freezers in particular are prime candidates. This is because for a split second after the supply is disconnected the appliance capacitor holds on to a charge, so the tester still sees a voltage even though the RCD has operated.
 

Reply to Faulty RCD tripping on the button but not via the tester in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
789
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
881
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock