Doing a EICR in a rental today and presented with this.

installation date is 1992 and there seems to be no records since.

At some point in the recent past someone has added a electric shower circuit. Obviously a smash and grab merchant as no earth sleeve and it was the same in the pull switch.

The 32a MCB is the shower. Now I know a circuit supplying a location containing a bath or shower with no RCD is a C3

But something is irking me that with this being the shower itself then it should have a RCD so I am leaning to a C2. However I can’t seem to find anything to support that.

Before I go slapping an unsatisfactory on the EICR thought I’d garner option on here.
20A2EC9B-F2F4-46F0-9935-BC829D352878.jpeg
Ta in advance.

Raptor
 
Thought lack of rcd in a bathroom (room containing a bath and or shower) was a C2 now

unless supplementry bonding was present and varified
 
Thought lack of rcd in a bathroom (room containing a bath and or shower) was a C2 now

unless supplementry bonding was present and varified

Bonding is in place on the gas and all the water pipes as I checked and tested them. Tenant nearly fell over my wander lead twice, despite it being bright green and me warning her ?
 
The manufacturers installation instructions in recent years for any shower will likely say an RCD MUST be installed. If that is the case, then C2.
Just found them online. So that’s a C2 then as you say. Thanks. ????

Plus it should be on a 40a MCB not a 32 as per their instructions.

At least I have something as evidence now for the landlord and estate agent.

D8155AD5-36ED-4F0B-9F0B-6A28C362CCD3.jpeg
 
It is not a requirement, only if circuit installation methods specify it, the manufacturer is misrepresenting the regulations although the regulations also say follow manufacturer's guidelines but they have not presented the guidance in that manner, they have clearly not understood current regulations. If they expressed rcd cover is required then that would have been within guidance of the regulations but they stated a false fact to come to the same requirement.
 
It is not a requirement, only if circuit installation methods specify it, the manufacturer is misrepresenting the regulations although the regulations also say follow manufacturer's guidelines but they have not presented the guidance in that manner, they have clearly not understood current regulations. If they expressed rcd cover is required then that would have been within guidance of the regulations but they stated a false fact to come to the same requirement.
Doesn't say a requirement of wiring regs. Just 'a requirement', so presumably a requirement of their own.

I would give it a C2 for the lack of RCD, and a C3 for the under rated breaker.
 
C2 on n my watch. reason...you have to allow for stupid: .a C2 unsatisfactory worst case is the customer/landlord will need to spend a few quid. A C3 and then nsomeone gets injured, it' s up befoer the judge for sparky. CYA.
 
In full agreement Tel, we should be working / assessing an installation to ensure it complies to the highest safety standards

lack of rcd nowadays is not satisfactory especially not in bathrooms/ showerooms

the person doing the eicr should ask themselves would I install a new power shower without putting it on an rcd , I hope not
 
You wouldn’t do it now, but you might need to know when the shower was installed, to see if it was a requirement then. There might be a manufacturing date inside.

Speak to the landlord before completing the eicr, and suggest a board change. Get everything covered by rcd that now needs it. He gets his satisfactory eicr on completion.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Shropshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Electric shower and no RCD
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Raptor0014,
Last reply from
littlespark,
Replies
9
Views
14,109

Advert

Back
Top