Evening all.

Doing a EICR in a rental today and presented with this.

installation date is 1992 and there seems to be no records since.

At some point in the recent past someone has added a electric shower circuit. Obviously a smash and grab merchant as no earth sleeve and it was the same in the pull switch.

The 32a MCB is the shower. Now I know a circuit supplying a location containing a bath or shower with no RCD is a C3

But something is irking me that with this being the shower itself then it should have a RCD so I am leaning to a C2. However I can’t seem to find anything to support that.

Before I go slapping an unsatisfactory on the EICR thought I’d garner option on here.
20A2EC9B-F2F4-46F0-9935-BC829D352878.jpeg
Ta in advance.

Raptor
 
Thought lack of rcd in a bathroom (room containing a bath and or shower) was a C2 now

unless supplementry bonding was present and varified
 
Thought lack of rcd in a bathroom (room containing a bath and or shower) was a C2 now

unless supplementry bonding was present and varified

Bonding is in place on the gas and all the water pipes as I checked and tested them. Tenant nearly fell over my wander lead twice, despite it being bright green and me warning her ?
 
The manufacturers installation instructions in recent years for any shower will likely say an RCD MUST be installed. If that is the case, then C2.
Just found them online. So that’s a C2 then as you say. Thanks. ????

Plus it should be on a 40a MCB not a 32 as per their instructions.

At least I have something as evidence now for the landlord and estate agent.

D8155AD5-36ED-4F0B-9F0B-6A28C362CCD3.jpeg
 
It is not a requirement, only if circuit installation methods specify it, the manufacturer is misrepresenting the regulations although the regulations also say follow manufacturer's guidelines but they have not presented the guidance in that manner, they have clearly not understood current regulations. If they expressed rcd cover is required then that would have been within guidance of the regulations but they stated a false fact to come to the same requirement.
 
It is not a requirement, only if circuit installation methods specify it, the manufacturer is misrepresenting the regulations although the regulations also say follow manufacturer's guidelines but they have not presented the guidance in that manner, they have clearly not understood current regulations. If they expressed rcd cover is required then that would have been within guidance of the regulations but they stated a false fact to come to the same requirement.
Doesn't say a requirement of wiring regs. Just 'a requirement', so presumably a requirement of their own.

I would give it a C2 for the lack of RCD, and a C3 for the under rated breaker.
 
C2 on n my watch. reason...you have to allow for stupid: .a C2 unsatisfactory worst case is the customer/landlord will need to spend a few quid. A C3 and then nsomeone gets injured, it' s up befoer the judge for sparky. CYA.
 
In full agreement Tel, we should be working / assessing an installation to ensure it complies to the highest safety standards

lack of rcd nowadays is not satisfactory especially not in bathrooms/ showerooms

the person doing the eicr should ask themselves would I install a new power shower without putting it on an rcd , I hope not
 
You wouldn’t do it now, but you might need to know when the shower was installed, to see if it was a requirement then. There might be a manufacturing date inside.

Speak to the landlord before completing the eicr, and suggest a board change. Get everything covered by rcd that now needs it. He gets his satisfactory eicr on completion.
 

Reply to Electric shower and no RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock