S spinna Mar 27, 2012 #16 Not sure to be honest the property was empty when i was doing the work there
P plugsandsparks ~ Esteemed Arms Mar 27, 2012 #20 was wondering if it worked but guess the shower had not been used for a while. Would have thought it would have "blown" almost immediately especuially if they tried to switch it off when under load. Hey ho
was wondering if it worked but guess the shower had not been used for a while. Would have thought it would have "blown" almost immediately especuially if they tried to switch it off when under load. Hey ho
G GLENNSPARK Mar 27, 2012 #21 so given the new colours.....was this `install` RCD protected....i know its besides the point but......
so given the new colours.....was this `install` RCD protected....i know its besides the point but......
P pencilpusher Mar 27, 2012 #22 "Its a 10A metal clad light switch used as a isolation switch for a shower fed via a 30A fuse and the circuit had no RCD protection" Apparently not
"Its a 10A metal clad light switch used as a isolation switch for a shower fed via a 30A fuse and the circuit had no RCD protection" Apparently not
G Guitarist Mar 27, 2012 #24 It had obviously worked for a while judging by the discoloured choccy block...