Hi guys is there any regulations regarding 110v centre tapped transformer transformer circuits being used outside (rcd protected) also if the transformer states 3000Va but a continuous rating of 1650Va am I right in thinking it can only carry 15amps before the transformer overloads?
A transformer will often have a continuous and intermittent rating. The continuous rating is a load which can be applied without the transformer suffering detrimental effect in your case 15A. You can exceed this to the transformers maximum load of 27A however not for a continuous period, this would be its intermittent rating.
EN61558 specifies a 25% duty cycle e.g. 5 minutes on and 15 minutes off for power tool transformer intermittent ratings. Since the copper loss is proportional to the square of the load current, and assuming the duty cycle to be approximately the reciprocal of the heat dissipation when under load, the intermittent rating will be approximately 1/(sqrt (0.25)) = 2 * continuous rating. So a 1.65kVA continuously rated transformer will offer a power tool intermittent (25% duty) rating of around 3.3 kVA. For those 5 minute periods it will deliver 30A and the wiring and OCPD needs to allow for this.
What are we relying on for earth fault on this style transformers the primary fuse?
Very often there will be fuses or MCBs in the secondary too, certainly on the larger transfomers that offer multiple sockets. The kiosk type used on construction sites have what is in effect a complete secondary side DB built in. Secondary protection of CT-E supplies obviously needs to be DP because neither wire of the load circuit is an earthed neutral.
I was thinking this type? I have seen the ones with a double pole breaker.
Those, like the yellow portable jobs, usually have a thermal CBE in the primary. I'm not a great fan of the type of CBE normally fitted, a bit flimsy and basic IMHO, but should track the thermal limit of the trafo better than any fuse.
Reply to 110v fixed wall mounted transformer in the UK Electrical Forum area at ElectriciansForums.net
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Hi lads, have not posted for some time, I have a question that I need to ask before I start a task I have been assigned to carry out this week...
Just trying to try get my head round these 110v wall mounted transformer I have come across. How comes the second side is unfused? Is there any...
4K
With regards to Regulation 531.3. 3 of BS 7671:2018+A2:2022 Older AC type RCD's are prone to being blinded by dc leakage from other items plugged...
6K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...