S
Silly Sausage
which is about EICs. what's that got to do with it?
Colour blind geordie...he's looking in the red book!

which is about EICs. what's that got to do with it?

Colour blind geordie...he's looking in the red book!![]()
If the appliance draws more than 16amp it shouldn't have a 16amp plug fitted.In my opinion, no one should be installing a 16A socket on a 20A MCB. This means an appliance could draw 20A through a plug and socket that is only rated at 16A! There are no fuses in these plugs like domestic ones don't forget.
If the appliance draws more than 16amp it shouldn't have a 16amp plug fitted.
Take a peek at p.160 OSG mate.

Well you live and learn. I still don't like the idea, a device rated at 16A can stil be expected to carry 20A.
Maybe I am just over cautious![]()

Why don't you just fit a 20 amp rotary isolator and hard wire it in. Fit a type C 20 amp MCB Job done. After all if you fit a 16 amp socket it has to be protected by an RCD or RCBO.Hi all, hopefully just a quick one.
Been asked to install a 16a commando socket in commercial premises for table saw.
It will be on a dedicated 20A radial cct.
Although the appliance is rated at 15A, it does state to allow for currents of up to 18A for start-up.
So my question is relating to the commando socket, would a 16A socket be considered suitable, will it handle the 18A short term current?
Or should I be specifying a 32A commando socket?
Opinions please?
Why don't you just fit a 20 amp rotary isolator and hard wire it in. Fit a type C 20 amp MCB Job done. After all if you fit a 16 amp socket it has to be protected by an RCD or RCBO.
Reg 411.3.3[/B][/I]
why??????
Reg 411.3.3
Socket outlets with a ratted current not exceeding 20 amps that are for use by on ordinary person should be protected by an RCD